Configuring a Johnson Controls BMS to truncate some least significant digits in received value transmitted by our energy meter

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Configuring a Johnson Controls BMS to truncate some least significant digits in received value transmitted by our energy mete...
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
sesa253061_brid
sesa253061_brid Cadet
Cadet

Posted: ‎2014-04-30 06:12 AM

0 Likes
0
838
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-30 06:12 AM

Configuring a Johnson Controls BMS to truncate some least significant digits in received value transmitted by our energy meter

Hello All,

Greetings from Power Monitoring team - Bangalore, India!

There's a customer in Malaysia who is using our PM1200 Energy meter with a Johnson Controls Building Management System (I have asked for the exact tool that they are using, version info, etc.). For zero current and voltage, our meter reads zero on its display but transmits a very small non-zero value (of the order of 10^-18) through its RS485 communication. Protocol used is MODBUS, data type is FLOAT32. This miniscule non-zero value is present because of some limitation in the calculation algorithm used in the meter.

The customer wants to read an exact zero through communication in the absence of current and voltage. We have asked him to configure his BMS to truncate the last few (least significant) digits from the received value. Doing so will give an exact zero as desired. But he seems to be having trouble following this.

I am not familiar with the Johnson Controls BMS, but I believe there must be some way to configure the tool to truncate least significant digits from a received value. Is there someone who is aware of the Johnson Controls BMS tool and can help me understand / guide me how to configure it so that it will truncate some least significant digits in received value (transmitted by our energy meter)?

Thanks & Regards,

Sutanu.

Tags (3)
  • Tags:
  • bms
  • building_management_system
  • johnson_controls
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of