Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION7300, PF sign convention

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION7300, PF sign convention
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
sesa213753
sesa213753 Leader
Leader

Posted: ‎2014-04-23 09:35 AM

0 Likes
8
3445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-23 09:35 AM

ION7300, PF sign convention

Hello, about ION7300,

Can the customer choose IEEE or IEC in ION7300 model meter ?

I found this in the document "ION Reference - 70002-0290-04 09/2011"

"PF Sign Convention

This register determines which sign convention, IEEE or IEC, is used for the PF Sign a, PF Sign b, PF Sign c and PF Sign tot output registers, and therefore how it is displayed on the front panel when the PF Symbol register in the Display Options module is set to “+/–”. The options are IEEE or IEC; see “Power Factor, Power and Energy Interpretation” for more details on how power factor is interpreted."

This apply for the ION7300 too ?

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa329134_brid
sesa329134_brid Leader
Leader

Posted: ‎2014-04-28 11:04 AM

0 Likes
3
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-28 11:04 AM

This is the print screen of the Power Meter Module of an ION7350, Firmware V284 (Latest), the PF Sign Convention is not availabe for the ION73X0 series.


3517

See Answer In Context

Reply
Replies 8
jimbradley
jimbradley Leader
Leader

Posted: ‎2014-04-23 10:06 AM

0 Likes
2
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-23 10:06 AM

Hi,

The answer is yes. 

This is an illustration of the "power of ION". 

Any product that is a "true" ION device will behave as per the documentation as the code/functionality is common across product lines.

Jim

Reply
sesa56307_bridg
sesa56307_bridg Troubleshooter
Troubleshooter

Posted: ‎2014-04-23 05:05 PM

1 Like
1
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-23 05:05 PM

I would suggest validating this to be sure.  I thought this setup register was only available on meters in our Advanced offer range (ION7550/7650, ION8650, etc).

Regarding the comment about the "power of ION", there are some cases where certain meters will implement only a subset of the setup registers associated with a given type of ION module.  In this case, I believe the ION7300 does not have the "PF sign convention" setup register on the Power Meter module, while other meter types (e.g. ION7650) do have this register.  I did a quick check on an ION7300, and I did not see this register myself.  There is definitely a common subset of registers that are implemented the same way on the different ION meters, but I think this is one of those cases where the available registers differ.

I may be mistaken, maybe there is a firmware version on the ION7300 that has this register?  But please don't assume that every meter type will have every ION register on the modules that it supports, because there are definitely exceptions.

Thanks,

David

Reply
sesa213753
sesa213753 Leader
Leader

Posted: ‎2014-04-24 02:03 PM

0 Likes
0
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-24 02:03 PM

HI May you help us ?

Reply
sesa213753
sesa213753 Leader
Leader

Posted: ‎2014-04-28 09:12 AM

0 Likes
4
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-28 09:12 AM

Hi   please, may you help me ?

Reply
sesa329134_brid
sesa329134_brid Leader
Leader

Posted: ‎2014-04-28 11:04 AM

0 Likes
3
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-28 11:04 AM

This is the print screen of the Power Meter Module of an ION7350, Firmware V284 (Latest), the PF Sign Convention is not availabe for the ION73X0 series.


3517

Reply
sesa213753
sesa213753 Leader
Leader

Posted: ‎2014-04-28 11:09 AM

0 Likes
0
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-28 11:09 AM

Thanks

Reply
sesa213753
sesa213753 Leader
Leader

Posted: ‎2014-04-28 11:11 AM

0 Likes
1
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-28 11:11 AM

Hey Alejandro, and do you know which options is pre-configured IEEE or IEC in the ION73X0 meters ?

Reply
sesa329134_brid
sesa329134_brid Leader
Leader

Posted: ‎2014-04-28 01:30 PM

0 Likes
0
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-28 01:30 PM

Not so sure, but I believe is the IEEE. This needs to be confirm by the Product Manager/R&D people.

Tks

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore