Co2 calculations in energy meter

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Co2 calculations in energy meter
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
527
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
139
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
p_dejarmy_encos
Lieutenant p_dejarmy_encos
Lieutenant

Posted: ‎2020-01-29 09:54 AM

0 Likes
4
1977
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-29 09:54 AM

Co2 calculations in energy meter

A client is requesting a metering system for many production lines (~70) and they want the metering system to include the calculaton of equivalent Co2 tons. They're looking for a system as cheap as possible, so PME is not in the scope of the project. Is there a way to calculate these values directly in a power meter (PM51XX) and report them back to the client?

 

Thanks.

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-01-31 08:54 AM

4 Likes
3
1974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-31 08:54 AM

Hi Pablo,

 

The PM5XXX series lacks the ION Logic to allow for CO2 calculations in the meter, but a PM8000 can achieve this no problem with an arithmetic module!

 

ION Setup is your best bet for programming the calculation on-site, unless you have your own PME system to create a framework in Designer and then load the DCF onto the meter on-site via ION Setup. 

 

The PM8000 has several means of getting the data out; Modbus RTU/TCP, Analog/Digital Output, Email. 

 

Modbus or Analog/Digital Out to their DCS or other software would likely be easiest to coordinate with E&I techs, but could require physical wiring beyond just Ethernet comms.

If their IT is both savvy and willing to help then SMTP email shouldn't be hard to set up either through the Alert Module. 

 

All-in-all it's pretty easy to get the calculation done, and a couple ways of getting the data out, just depends on the customers preferred format. 

 

 

Best of luck!

 

– Scott Clysdale

See Answer In Context

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-04 05:11 PM

2 Likes
0
1966
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-04 05:11 PM

Hello,

 

While the PM8000 has up to 64 modbus device modules, I do not think you can have all ~60 device on a single Rs-485 loop. I guess your next question would be how many can I have on a loop and I do not know for sure, there are things like burden of each RS-485 interface on PM5000 or iEM to consider.

 

I have never tried loading a meter this high so I cannot say what the performance would be like. Could also look at have multiple gateways connected to a group and meters and have the (or multiple) PM8k modbus master via the gateway.

 

Charles

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 4
Anonymous user
Not applicable

Posted: ‎2020-01-31 08:54 AM

4 Likes
3
1975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-31 08:54 AM

Hi Pablo,

 

The PM5XXX series lacks the ION Logic to allow for CO2 calculations in the meter, but a PM8000 can achieve this no problem with an arithmetic module!

 

ION Setup is your best bet for programming the calculation on-site, unless you have your own PME system to create a framework in Designer and then load the DCF onto the meter on-site via ION Setup. 

 

The PM8000 has several means of getting the data out; Modbus RTU/TCP, Analog/Digital Output, Email. 

 

Modbus or Analog/Digital Out to their DCS or other software would likely be easiest to coordinate with E&I techs, but could require physical wiring beyond just Ethernet comms.

If their IT is both savvy and willing to help then SMTP email shouldn't be hard to set up either through the Alert Module. 

 

All-in-all it's pretty easy to get the calculation done, and a couple ways of getting the data out, just depends on the customers preferred format. 

 

 

Best of luck!

 

– Scott Clysdale

Reply
p_dejarmy_encos
Lieutenant p_dejarmy_encos
Lieutenant

Posted: ‎2020-02-04 08:01 AM

0 Likes
2
1968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-04 08:01 AM

Hello @Anonymous user thanks for your response.

 

Since there are many devices to be metered (~60 circuits) I'm thinking about using a PM5100 or even iEM3255 for each circuit.

 

If I use a PM8000 as a "main" meter and all of the PM5100 are connected via RS485 (daisy chain) to the PM8000, can their inputs be used on the meter's designer frame? I've done this many times on PME, but never directly on the meter.

 

Thanks in advance.

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-04 05:11 PM

2 Likes
0
1967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-04 05:11 PM

Hello,

 

While the PM8000 has up to 64 modbus device modules, I do not think you can have all ~60 device on a single Rs-485 loop. I guess your next question would be how many can I have on a loop and I do not know for sure, there are things like burden of each RS-485 interface on PM5000 or iEM to consider.

 

I have never tried loading a meter this high so I cannot say what the performance would be like. Could also look at have multiple gateways connected to a group and meters and have the (or multiple) PM8k modbus master via the gateway.

 

Charles

 

L4 Prime for Advanced metering and Utilities
Reply
Anonymous user
Not applicable

Posted: ‎2020-02-05 02:00 PM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-05 02:00 PM

Hi @p_dejarmy_encos,

 

Feeding inputs into a PM8000 Modbus Master is a viable solution. 

 

Perhaps look at the EM4800/EM4000 multi-circuit meter – each meter can take in 24 current inputs, and 3 voltage inputs (8 total 3Φ loads), perfect for panel monitoring, and lowering costs. 

 

This would also reduce the number of Modbus Master modules needed on the PM8000 by a factor of 8. I would heavily suggest using Modbus TCP on Ethernet as well, to avoid using serial.

 

 

Regards,

 

– Scott Clysdale

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore