Posted: 2016-08-25 05:06 AM
Link copied. Please paste this link to share this article on your social media post.
I don't see that it does this so next question is: how EASY would it be to add this information into the QR code ?
Presently our meter installers have to validate the meter was wired correctly by connecting to the meter with ION Setup and saving the Phasor plot via a PC.
The QR code would make capturing this important information much easier for them.
Thanks for giving it some thought!
Greg.
Link copied. Please paste this link to share this article on your social media post.
Hi Greg,
That's a great question for a very valid use-case. The QR codes don't presently bring in phasor information; we would need to do a firmware update for adding a new Phasor QR screen and develop the complimentary support in the Meter Insights webservice. Not trivial but possible
I should highlight that we've actually already built a notification within Meter Insights if the device appears to be mis-wired (by interpreting the PF reading); the user simply has to scan the Info, PQ or Min/Max QR screen. If you wanted, I would be happy to discuss the value of this existing capability with some installers so that we can confirm if/how to improve it further
Thanks
sam
Link copied. Please paste this link to share this article on your social media post.
Hi Greg,
That's a great question for a very valid use-case. The QR codes don't presently bring in phasor information; we would need to do a firmware update for adding a new Phasor QR screen and develop the complimentary support in the Meter Insights webservice. Not trivial but possible
I should highlight that we've actually already built a notification within Meter Insights if the device appears to be mis-wired (by interpreting the PF reading); the user simply has to scan the Info, PQ or Min/Max QR screen. If you wanted, I would be happy to discuss the value of this existing capability with some installers so that we can confirm if/how to improve it further
Thanks
sam
Posted: 2016-08-25 08:39 PM
Link copied. Please paste this link to share this article on your social media post.
Thanks for the reply Sam.
We have an existing solution using ION Setup to capture and save the phasor of a meter.
But that requires using a PC & software.
The QR would have been quite elegant if it had the phasor data already in it.
We're good with the software solution.
Thanks again.