IN the user manual says:
"MIB files
Your meter is compliant with MIB-II as defined by the standard MIB file RFC 1213.
SNMP requires that you load your meter’s ION MIB file (available for download
from www.schneider-electric.com) into the NMS.
You must install RFC 1213, which is required to read basic network information for
the meter (for example, TCP/IP traffic or number of packets received), if it is not
included with your SNMP manager software."
But i cant find it.
best regards
Link copied. Please paste this link to share this article on your social media post.
Hi Jorge,
These are generally posted alongside the firmware release and will be on the web for the next firmware release for the ION7400. For now, I have attached it to this message for you to use. I hope this helps.
Regards,
Sanjeet
Link copied. Please paste this link to share this article on your social media post.
Hi Jorge,
These are generally posted alongside the firmware release and will be on the web for the next firmware release for the ION7400. For now, I have attached it to this message for you to use. I hope this helps.
Regards,
Sanjeet
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.