Hi,
We have a client request to monitor the temperature of there busbar's within a Data Centre. Each busbar has a PM8240, so we are thinking of adding a Analog card to each PM8240, and wire 4 (A:B:C:N) temperature sensors into it.
Can anyone recommend a wired (wireless is a no no within our clients DC's?) temperature sensor that is suited for measuring the temperature on a busbar?
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
PME2020 introduced a new thermal monitoring driver for the Exertherm ARM XL device:
https://exertherm.com/applications/lv-switchgear/
The "Datacards" the ARM XL uses are actually serial Modbus devices that could be connected as slave devices on a PM8000's serial port if you don't need the HMI. The Modbus map is fairly simple, and the power of ION would make it straightforward to integrate. These Datacards support several different types of sensors too - and they're wired.

Posted: 2020-02-18 02:28 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello, the community members can you help this member on this topic, please?
@Charles_M do you think you can advise on this topic?
@nigel_greenwave if you still haven't found a solution please do not hesitate to inform us here.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
By using Type-K or any thermocouple connect to Analog input then convert to temperature.
See ION Reference on Analog Input Module and Arithmatic Module use Type-K or other linearization function.
This is the beauty of ION meter in which you can do customization.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Just be sure to take adequate precaution to ensure required safety & electrical isolation barriers are in place between the busbar and thermocouple... Those Analog inputs are low voltage and not rated for bus bar voltages.
Google searches show several 3rd party wired modules for this application (thermo couple output, analog 4-20mA, modbus, etc), however I could only find wireless offers from SE.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
What we are planing do to, is to try is using a 4-20ma contact temperature sensor and strapping it on the cable near the copper connection point (60-80mm away from the copper). If there is a lose connection or over loading the cable should heat up.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi have checked with Canalis and OKKEN Marketing and they do not have specific recommendation concerning temperature sensors for their offers.
Currently, the best solution pushed by Marketing is to use TH110 or CL110 sensors with ZBRN32 or PowerTag Link... but this is a Wireless solution.
Regards,
Romain
Solution Architect - France Operations

Posted: 2020-04-09 02:24 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi @nigel_greenwave,
Did you find your answer to the replies above?
If yes, please click on "Accept as Solution" at the bottom right corner of the answer which helps you.
You can also thank the members who tried to help you by liking their comments!
Have a nice day.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
PME2020 introduced a new thermal monitoring driver for the Exertherm ARM XL device:
https://exertherm.com/applications/lv-switchgear/
The "Datacards" the ARM XL uses are actually serial Modbus devices that could be connected as slave devices on a PM8000's serial port if you don't need the HMI. The Modbus map is fairly simple, and the power of ION would make it straightforward to integrate. These Datacards support several different types of sensors too - and they're wired.