Posted: 2017-09-08 09:43 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
My short answer is that all of these registers (PF sign, PF lead, PF lag) are different formats for what amounts to total power factor (by definition, based on the full measurement bandwidth); none of them correspond to displacement power factor (by definition, based on the fundamental component only). If you are interested in the displacement power factor, it would be possible to derive it in the ION framework using data from the Power Harmonics module, but that requires some custom ION programming and it is not available in the default ION framework for the ION7650. The PM8000 does provide this measurement in its default ION framework, and the logic would be similar for the ION7650.
For your understanding, here is a brief description of the existing registers. "PF sign" provides a signed value between -100 and 100, where the sign convention is configurable as either IEEE (leading=+, lagging=-) or IEC (follows the sign of real power). "PF lead" is an unsigned value (either 0 to 100 for leading power factor or N/A for lagging power factor). "PF lag" is also an unsigned value (either 0 to 100 for lagging power factor or N/A for leading power factor).
I would recommend the "ION Reference" document as a resource to help with this type of question, looking specifically at the description for the Power Meter module for this topic:
ION Reference -EN | Download Schneider Electric
Here are some excerpts from that document, referring to the descriptions within the "Power Meter module".




Link copied. Please paste this link to share this article on your social media post.
All registers on 7650 or all the measurements being logged? 7650 has thousands of registers. What is the application you are trying to do?
Posted: 2017-09-10 09:08 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Huang,
I want know name register Power Factor Displacement in ION7650?, because I see in ION7650 have PF sign, PF Leading, PF Lagging.
More can you explain difference PF Leading and PF Lagging.
Thanks very much
Link copied. Please paste this link to share this article on your social media post.
David Tuckey, can you explain the difference between PF Leading and Lagging?
Posted: 2017-09-11 10:28 AM
Link copied. Please paste this link to share this article on your social media post.
HI Huang,
Thanks very much
HI Tuckey
Please help me
Thanks very much
Link copied. Please paste this link to share this article on your social media post.
My short answer is that all of these registers (PF sign, PF lead, PF lag) are different formats for what amounts to total power factor (by definition, based on the full measurement bandwidth); none of them correspond to displacement power factor (by definition, based on the fundamental component only). If you are interested in the displacement power factor, it would be possible to derive it in the ION framework using data from the Power Harmonics module, but that requires some custom ION programming and it is not available in the default ION framework for the ION7650. The PM8000 does provide this measurement in its default ION framework, and the logic would be similar for the ION7650.
For your understanding, here is a brief description of the existing registers. "PF sign" provides a signed value between -100 and 100, where the sign convention is configurable as either IEEE (leading=+, lagging=-) or IEC (follows the sign of real power). "PF lead" is an unsigned value (either 0 to 100 for leading power factor or N/A for lagging power factor). "PF lag" is also an unsigned value (either 0 to 100 for lagging power factor or N/A for leading power factor).
I would recommend the "ION Reference" document as a resource to help with this type of question, looking specifically at the description for the Power Meter module for this topic:
ION Reference -EN | Download Schneider Electric
Here are some excerpts from that document, referring to the descriptions within the "Power Meter module".