A9MEM3255 energy meter giving inconsistent data in 3Ph4w with 3 CT connection

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • A9MEM3255 energy meter giving inconsistent data in 3Ph4w with 3 CT connection
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Sabyasachi
Sabyasachi
Cadet

Posted: ‎2024-03-13 10:43 PM

0 Likes
3
601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-03-13 10:43 PM

A9MEM3255 energy meter giving inconsistent data in 3Ph4w with 3 CT connection

Hi All, 

I have been trying to read the registers of Active power(p1,p2,p3) and energy(p1,p2,p3), of the Float32 format, using RS485 communication.

I have configured the setting on SE meter to run as 3ph4Wire system, with 3 CTs, No VT connection, with all the CTs having the turns ratio of 100/5, I am aware that, we are supposed to configure the CT ratios in the  meter itself, and I have done so, keeping Secondary turns 5 and Primary turns 100.

Even the wiring is done according to what is mentioned in the Datasheets, 

I tried reading all individual phase voltage, individual phase currents, and I'm getting the data correctly.

All the 3 CTs are connected to the same 200 W bulb.

When I'm trying to read the individual float32 active power registers, for phase 1 , i'm getting a value of 0.19879496097564697 Kw , phase 2 : 0.10172723978757858 Kw, phase 3 : 0.10699596256017685 Kw.

Where I should be getting values of all 3 phases as around 0.200 Kw, so, the phase 1 seems to be somewhat accurate, however phase 2 and phase 3 are not. Even though all the CTs are connected in same direction.

The total active power that was showing on the screen itself was around 400 Watts.

Could somebody help me out with this problem.

Thanks and regards.

 

 

Labels
  • Labels:
  • iEM3000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2025-01-07 06:49 AM

0 Likes
0
213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-07 06:49 AM

Hi @Sabyasachi 

Please connect with country technical support team with all 3 CTs secondary current values, if this query is not addressed yet, the CT secondary current value will be around 5mA for 200W load current. Please check CT1, CT2 and CT3 secondary values and connect with the country technical team. 

See Answer In Context

Reply
Replies 3
Jesus_Diaz
Lt. Commander Jesus_Diaz Lt. Commander
Lt. Commander

Posted: ‎2024-03-15 11:10 AM

0 Likes
0
573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-03-15 11:10 AM

Hi @Sabyasachi,

 

Can you increase the load and re-check? Usually, it is recommended to try with at least 10% of the rated current of the CT.

 

Also, I would suggest connecting to the meter using ION Setup and getting all the measurements (currents, voltages, power, per phase) from the meter to have a better understanding.

 

Best regards.

Reply
Sabyasachi
Sabyasachi
Cadet

Posted: ‎2024-06-19 05:56 AM

0 Likes
1
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-19 05:56 AM

Hi @Jesus_Diaz ,

How come for the CT1 , we are getting proper, nearly accurate values?

And why for only CT2 and CT3 are we facing this problem?

Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2025-01-07 06:49 AM

0 Likes
0
214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-07 06:49 AM

Hi @Sabyasachi 

Please connect with country technical support team with all 3 CTs secondary current values, if this query is not addressed yet, the CT secondary current value will be around 5mA for 200W load current. Please check CT1, CT2 and CT3 secondary values and connect with the country technical team. 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of