400 Hz Nominal on PM8000

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

aaron_azzo_com_
Ensign
Ensign
0 Likes
3
240

400 Hz Nominal on PM8000

All, I'm urgently trying to determine how/why I the 400Hz nominal frequency cannot be selected in the PM8000.  We've tried through the HMI, webpage, ION Setup and Designer.  In Designer, the 400Hz is greyed out, which suggests it's available, but not available right now.  The PM820 has the 400Hz option available, and it can be simply done through the HMI if required; the PM8000, being a higher end meter, needs to have this issue worked out, or else the operating range needs to be changed in the documentation to show it's only able to work in 50/60Hz environments.  I need to rectify this today if possible.

Thanks,

Aaron.

Tags (3)
3 Replies 3
Sam_Gaib
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
174

Re: 400 Hz Nominal on PM8000

Hi Aaron: ARNAUD DENIS is the PM8000 Offer Manager who could confirm for you

sesa142768_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
1
174

Re: 400 Hz Nominal on PM8000

Hi Aaron,

I did reply through email but failed to see this community request. Thanks Sam for pointing it out.

The PM8000 will measure at 400Hz but you cannot select it through the menu. If you set the meter at either 50Hz or 60Hz, the meter will detect the 400Hz and report accordingly.

The following values will be measured correctly: Vln, Vll, kW, kVAR, kVA, PF, Freq

However, the all PQ measurements will be incorrect due to the Harmonics being sampled at 50/60Hz. This restriction is partly hardware based.

Regards

aaron_azzo_com_
Ensign
Ensign

Re: 400 Hz Nominal on PM8000

Thanks for the information Denis.

Unfortunately as the PM8000 is not sold as an entry level meter, the PQ measurements need to be accurate and available when on a 400/60/50Hz system.  Also, the displacement power factor will be adversely affected as it's based on the fundamental frequency, so PF is not truly available, unless you're referring to only the TPF.

Do you have an ETA when this will be rectified?  Or if the meter will not be 400Hz compliant, then the marketing and tech material should be changed (as discussed with a while back) to reflect the discrepancy to reduce negative customer feedback and experience.

Regards,

Aaron.