Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

16-32 Load profile Channels with ION Setup

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • 16-32 Load profile Channels with ION Setup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Natalie
Natalie
Explorer

Posted: ‎2025-06-30 11:32 AM

0 Likes
3
1089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-30 11:32 AM

16-32 Load profile Channels with ION Setup

I am trying to configure 16+ load profile channels for an ION8650 in ION Setup and then retrieve them with the reporting tab.  The load profile report defaults to a maximum of 16 channels though-- is there a way to pull the report for more than 16 channels? 

Labels
  • Labels:
  • ION Setup
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-07-07 11:46 AM

1 Like
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-07 11:46 AM

Hello @Natalie ,

 

PME pulls data from all data recorders unless told to limit specific data recorders, default option is everything on the device. ION Setup, depends what version are where you are looking. Newer versions of ION Setup typically have most default data recorders added to View -> Data Screens -> Data Recorders. 

The Setup Assistant -> Reports view is defaulted to only look at specific data recorders. As with many things ION, there may be a way to customize what you see in ION Setup. Where ION Setup is installed (C:\Program Files (x86)\Schneider Electric\ION Setup) there is a folder called Tables. Inside this folder is folders for each device type, PML8650 for example for ION8650 meters. In Each device type folder there is one or more folders for the type of meter and firmware version, example Feature Set A V4.40. Inside this folder is another folder for data recorder configurations and a file QuickION.cfg. You can create custom .pml files to look at a data recorder. Or you can edit the QuickION.cfg file to add additional data recorders.

 

Note that you should backup any file before making changes. QuickION.cfg files has a section [Reports] where the ION handle of the data recorder can be entered. If you do not know what IOn handle is or where to find, do not edit the QuickION.cfg file.

Tab1Registers=7
Tab1Reg1=10,1,0x0F80,Revenue Log
Tab1Reg1Text=This shows the meter revenue log information.
...

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 3
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-07-02 07:42 AM

0 Likes
2
1075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-02 07:42 AM

Hello @Natalie ,

 

ION8650 meters support a maximum of 16 channels per data recorder module. Only ION9000.PM8000/ION7400 meters are ION meters that support up to 50 channels with V4.6.0 firmware.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Natalie
Natalie
Explorer

Posted: ‎2025-07-03 10:09 AM

0 Likes
1
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-03 10:09 AM

Hi Charles,

 

If I changed Data Rec 2 from Sag/Swell to be 16 more Revenue log load profile channels, is there a way to view the load profile report for Data Rec 1 and Data Rec 2 at one time? Or a way to choose which Data Rec # the report pulls data from, in ION Setup or PME?  

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-07-07 11:46 AM

1 Like
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-07 11:46 AM

Hello @Natalie ,

 

PME pulls data from all data recorders unless told to limit specific data recorders, default option is everything on the device. ION Setup, depends what version are where you are looking. Newer versions of ION Setup typically have most default data recorders added to View -> Data Screens -> Data Recorders. 

The Setup Assistant -> Reports view is defaulted to only look at specific data recorders. As with many things ION, there may be a way to customize what you see in ION Setup. Where ION Setup is installed (C:\Program Files (x86)\Schneider Electric\ION Setup) there is a folder called Tables. Inside this folder is folders for each device type, PML8650 for example for ION8650 meters. In Each device type folder there is one or more folders for the type of meter and firmware version, example Feature Set A V4.40. Inside this folder is another folder for data recorder configurations and a file QuickION.cfg. You can create custom .pml files to look at a data recorder. Or you can edit the QuickION.cfg file to add additional data recorders.

 

Note that you should backup any file before making changes. QuickION.cfg files has a section [Reports] where the ION handle of the data recorder can be entered. If you do not know what IOn handle is or where to find, do not edit the QuickION.cfg file.

Tab1Registers=7
Tab1Reg1=10,1,0x0F80,Revenue Log
Tab1Reg1Text=This shows the meter revenue log information.
...

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore