Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

"No license for LonWorks communication" Error in Windows 2008 Server X64

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • "No license for LonWorks communication" Error in Windows 2008 Server X64
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • SESA150559
    SESA150559
  • CraigEl
    CraigEl
  • sesa145087_brid
    sesa145087_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2182 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

"No license for LonWorks communication" Error in Windows 2008 Server X64

Picard Product_Support
‎2018-09-07 04:05 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 07:15 PM

Issue

"No license for LonWorks communication" Error when starting Workstation.

Product Line

TAC Vista

Environment

  • Windows 2008 Server X64
  • TAC Vista 5.1.5

Cause

  1. Windows Server is member of a domain.
  2. Configure the TAC Vista Server to run as a service, with a local user set as administrator to logon.

Results in "No license for LonWorks communication" when starting Workstation. If starting the service with a domain user or local system, it works. 

Resolution

Windows Security Policy

This may have something to do with UAC (User Account Control) in Windows. The user that launches TAC Vista was already as a local administrator, but it seems that a log out with the user, log in with a local user, and log back in with a domain user is necessary for some policies to be set.

Licensing Registry

The Vista licensing requires registry information on where to find a license file. This registry key is found in the following location:

HKEY_CURRENT_USER\Software\FLEXlm License Manager\TACLIC_LICENSE_FILE

If the user has not been logged in and configured to run Vista software, this key might be missing or misconfigured. Ensure that it has a proper value by launching Vista Workstation or running the TAC License Setup. Log in with the user that will run the TACOS service and run the License Server Setup application to ensure the correct file path is defined in the Registry.  


Related Articles:

  • "No license for LonWorks communication" with TAC Vista Server LE
  • "No license for LonWorks communication" error when using a non LE dongle
  • "No license for LonWorks communication" - LonMaker Recovery Folder
  • "No license for LonWorks communication" error message in Classic Network
  • "No license for LonWorks communication" in Vista Workstation
  • TACOS startup delay utility
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4321
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore