Webstation graphics not working after Java updated to Java 7 update 51

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Webstation graphics not working after Java updated to Java 7 update 51
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • sesa139513
    sesa139513
  • Gary
    Gary
  • LeeCravens
    LeeCravens
  • Benji
    Benji
  • Julio_Cortes
    Julio_Cortes
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3453 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Webstation graphics not working after Java updated to Java 7 update 51

Picard Product_Support
‎2018-09-11 05:22 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 07:40 PM

Issue

After updating the computers Java version to Java 7 update 51, graphics are not displayed when using Webstation.

Then a security warning is displayed.

Missing required Permissions manifest attribute in main jar: http://xxx.xxx.xxx.xxx:/com.SE.webstation.Main/applet/applet-1.4.1.68.jar

If you don't see the error above, but just get a blank window, please refer to Webstation graphics not working after updating to Java 7 Update 65.

Product Line

EcoStruxure Building Operation, Satchwell MicroNet, TAC Vista

Environment

Webstation

Cause

From Java 7 Update 51 and onwards, Java has enhanced the security model to make user system less vulnerable to the external exploits. The new version of Java does not allow users to run the applications that are not signed (Unsigned), Self signed (not signed by trusted authority) and the applications that are missing permission attributes.

Risks involved in running each kind of applications:

  • Unsigned applications
    An application without a certificate (i.e. unsigned apps), or missing application Name and Publisher information are blocked by default. Running this kind of application is potentially unsafe and present higher level of risk.
  • Self signed application (Certificate not from trusted authority)
    An application with self-signed certificate is blocked by default. Applications of this type present the highest level of risk because publisher is not identified and the application may be granted access to personal data on your computer.
  • Jar file missing Permission Attribute
    Permissions Attribute verifies that the application requests the permission level that developer specified. If this attribute is not present, it might be possible for an attacker to exploit a user by re-deploying an application that is signed with original certificate and running the application at a different privilege level.

Resolution

As a workaround, the user can use Exception Site list feature to run the applications blocked by security settings. By adding the URL of the blocked application to the Exception Site list allows it to run with some warnings.
Steps to Add URL to the Exception Site list:

  1. In control panel go to the Java Control Panel
  2. Click on the Security tab
  3. Click on the Edit Site List button
  4. Enter your site details (This example http://www.SBO-Site.com)
  5. Click the Add in the Exception Site List window.
  6. Select continue
  7. Repeat the process until all the sites AS/ES have been added.
  8. Then select OK to complete and OK on the next window to exit the Java control panel.
  9. Next time you use Webstation to access the AS/ES you will be asked if you want to run the application.
  10. Tick the box so this is not displayed again.
  11. Then select Run.

The graphics should now be displayed.

You will need to repeat this process on any computer you which to use Webstation on.

Labels (3)
Labels:
  • EcoStruxure Building Operation
  • Satchwell MicroNet
  • TAC Vista
Tags (4)
  • Find more articles tagged with:
  • 13698
  • 23661
  • alm
  • defect
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore