Issue
- After updating Java (e.g., to Java 7 Update 65 or later), WebStation graphics may appear blank or white.
Note: If the error you see is “Error. Click for details” and not a blank window, please refer to the article: WebStation graphics not working after Java updated to Java 7 Update 51.
- Customers also need clarity on when Java was removed from WebStation and replaced by HTML5.
Product Line
EcoStruxure Building Operation, TAC Vista
Environment
- Java
- Building Operation WebStation
Cause
- Compatibility issues between Java and WebStation in TAC Vista or older Building Operation versions.
- Java applets were historically used for TGML graphics, causing security warnings and browser compatibility problems.
- Transition to HTML5 technology eliminated these issues.
Resolution
For Java-related issues (TAC Vista or SBO 1.5 and earlier)
-
Update Java
- Install the latest Java version (e.g., 1.7u67).
- On x64 systems, install both x86 and x64 Java versions.
-
If issue persists, perform clean reinstall:
- Close all browsers.
- Uninstall all Java versions.
- Backup
exception.sitesfile:C:\Users\<username>\AppData\LocalLow\Sun\Java\Deployment\security\exception.sites - Delete folder:
C:\Users\<username>\AppData\LocalLow\Sun - Reinstall latest Java (both x86 and x64 if applicable).
- Verify Java installation using Java uninstall applet.
- Restore
exception.sitesfile to its original location.
Technology Transition Note
-
Pre-2014 (SBO 1.0–1.5)
- TGML graphics displayed using Java applets.
-
2014–2015 (SBO 1.6)
- HTML5 Viewer introduced as Beta in WebStation.
- Users could enable HTML5 manually; Java remained default.
-
2015–2016 (SBO 1.7)
- HTML5 fully implemented as the default graphics viewer.
- Java completely removed from WebStation.
-
2017 onward (EBO 2.x and beyond)
- Modern HTML5 UI with responsive design.
- No plugins required; optimized for Chrome, Edge, Firefox.