Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Security Expert Error, Server Has Rejected Client Credentials

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Security Expert Error, Server Has Rejected Client Credentials
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support
  • AdamSteele
    AdamSteele
  • David_Kendrick
    David_Kendrick

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
9843 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Security Expert Error, Server Has Rejected Client Credentials

Picard Product_Support
‎2018-09-06 03:45 PM

Last Updated: Picard RobertAndriolo Picard ‎2021-11-30 01:32 PM

Issue

The following error can occur when logging into Security Expert using a Remote Client:

 

Could not log on to Server. Please check your remote connection setup. The server has rejected the client credentials.

SX_ClientLoginError_TheServerHasRejected (002).jpg

Product Line

EcoStruxure Security Expert

Environment

Security Expert Server / Client

Cause

The security policy settings are different between the Server and Client.

 

When installing the Security Expert Server and Clients, the default security policy is used. This requires that the Windows username and password that the operator has used to log in on a client machine is also a valid user on the computer that is running the Security Expert Server. These security requirements are very favourable for corporate networks and setups where the users and policies are easy to manipulate. For that purpose alone, the Security Expert Server and Client are installed with these settings by default.

 

All installations are not created equal however and sometimes the Security Expert Server is not located within a domain. In another scenario, the server may be in a domain but the operators need to connect to it from a machine that is not in the domain. In these cases, it has been requested that the security policy in place on a domain or the physical machine is disabled and although this is not recommended practice the security of the system can be maintained using a suitable VPN structure.

 

This solution should be used with full knowledge that the security of the system will rely on the operator user login name and password as well as the security measures put in place for a client to be able to hit the server with a login request. Protection of the infrastructure to the connection is beyond the scope of this document.

Resolution

The easiest solution would be to put the Client machine(s) in the same Domain as the Server.  However if this is not possible or if no Domain is used then you can still manually update the security policy instead.

The following process is a manual edit of the XML configuration files 

  • SecurityExpert.exe.config 
  • SecurityExpertSV.exe.config 

Both of these files are located in the .\Program Files\Schneider Electric\Security Expert directory on the Client and Server. It is recommended then to backup these two files prior to performing this task.

  1. Close all Security Expert clients and stop the Security Expert Data Service.
  2. We are first going to update the Security Expert Client configuration file SecurityExpert.exe.config on the client machine.  If using more than one Client, the change must be done for ALL clients
  3. Open Notepad as the administrator, browse to the specified location making sure the 'all files option' is selected.  Then open SecurityExpert.exe.config
    (Be aware that it may not have the file extension showing and will be called an XML Configuration file by default)
  4. Locate the netTcpBinding tag . Nested within this tag is the binding tag
    Ensure that you insert the below text after the opening binding tag and before the closing \binding tag . If you insert the text outside this tag, the application will fail to run.  

    "<security mode ="None"></security>"

  5. IMPORTANT You must ensure you enter "None" with a capital "N" (not lower case). Ensure you copy input text exactly as shown. Now save the file. If you get a write error then you need to open notepad as the administrator.
    client.png

  6. Repeat the process for the Security Expert Server configuration file SecurityExpertSV.exe.config which is located in the same directory on the server machine.     
    Again, make sure the line is inserted after the opening tag and before the closing tag or the application will fail to run when you save the changes.
    server.png
  7. Restart the Security Expert Data Service and test the connection settings.
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (5)
  • Find more articles tagged with:
  • 19543
  • AdamSteele23
  • DavidKendrick21
  • HernanUruena24
  • RobertAndriolo21
Was this article helpful? Yes No
100% helpful (5/5)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore