Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

SNMP Flashing options for Netcontrollers and BCXs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SNMP Flashing options for Netcontrollers and BCXs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1974 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SNMP Flashing options for Netcontrollers and BCXs

Picard Product_Support
‎2018-09-07 02:29 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:57 AM

Issue

SNMP Flashing options for Netcontrollers and BCXs

Product Line

Andover Continuum

Environment

All Continuum master controllers

Cause

Documentation

Resolution

BCXs & Netcontrollers can be in 3 states:

  1. SNMP Standard is how all controllers are shipped by default. This means that the controller model and some other object info can be obtained via SNMP.
  2. SNMP Alarming Enabled means Standard SNMP as well as SNMP Alarming is enabled in order to send alarms to a network management system. This is a paid for option either initially when the controller is ordered or by contacting repair. To enable this option in the field, repair sends a file and instructions after payment.
  3. SNMP Disabled means that no SNMP information will come from the controller.

Upgrading controllers with future firmware versions

Depending on which SNMP option state the controller is in will determine the application flash that should be used going forward. Selecting the incorrect file can disable or re-enable SNMP options.

Netcontroller

  • v1.5300x SNMP Not Set means no SNMP options will be changed when upgrading firmware
  • v1.5300x Standard SNMP means use with Standard SNMP (default)
  • v1.5300x SNMP Alarming Enabled means use when SNMP Alarming is enabled
    (Not Set could be used also since it will not change the enabled option)
  • v1.53 SNMP Disable means this will disable All SNMP traffic, Standard and Alarming

BCX

Use the default firmware upgrade after SNMP is enabled. If you use the BCX SNMP Disable flash files and then upgrade to a newer version of firmware, you will have to run the disable flash file again to disable SNMP.

NOTE: The flash files used to disable SNMP are posted on The Exchange.

Note2: If the flash file doesn't enable the options because it was sitting at resetting controller,  Reload the controller which will force a reset and then try the flash file again.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2861
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore