Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.

Configure Time Zone and UTC Offset settings so that time is synchronized across your system

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configure Time Zone and UTC Offset settings so that time is synchronized across your system
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • BillNeville
    BillNeville
  • AdamSteele
    AdamSteele
  • CraigEl
    CraigEl
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5692 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configure Time Zone and UTC Offset settings so that time is synchronized across your system

Picard Product_Support
‎2018-09-11 12:00 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:55 PM

Issue

How to properly configure Time Zone and UTC Offset settings in Cyberstations and controllers.

Product Line

Andover Continuum

Environment

  • Continuum Cyberstation
  • Continuum Controllers

Cause

There are a number of locations for time configuration settings, creating uncertainty as to what needs to be set, and where, to maintain the correct time in all devices.

Resolution

How to sync controller time with WS time with Server time.

Set the correct UTC offset (time zone) in all of the below locations:

  1. Confirm Cyberstation(s) PC time zone (UTC offset) and regional settings are correct. [This has no effect on time synchronization but does have an effect on what time alarms and events are written to the database as well as when alarms will be delivered to Cyberstations]
  2. Confirm the SQL Server PC time zone (GMT settings) and regional settings are correct. [same as 1 above]
  3. In Continuum, the Workstations Device object's Time tab has the correct time zone setting (be aware this is in minutes, ex. GMT+10 = +600 minutes.)
  4. In Continuum, the Network folder has a setting for the time zone, this needs to be configured to the time zone the controllers are located. If GMT+10 then this gets set to +600.

Note1: To synchronize controller time to Workstations time a program needs to be created in one WS that sets the Date object of the Netcontroller (IP level controller) with the lowest ACCnet ID. This controller will then push any time changes out to all other IP level controllers and down to its subnet controllers (i2’s or b3’s). See Time sync controllers to workstations for details on this.

Note2: At 38 minutes past the hour the Netcontroller will push its time down to its subnet (aka Field Bus) controllers.

Note3: When time is set in the Netcontroller with a reload of the controller, the UTC settings of the WS doing the reload, and the Network folder the controller is in, are accounted for and the controllers time is set with these UTC settings taken into account. When time is set with a PE program using the WS Date object, this does not take into account the UTC settings of the various locations and just sets the controller Date object to the exact value of the WS Date object. If the controller is in a different time zone than the WS setting its time, then it will now have the wrong time in it. To compensate for this, it is suggested that time offsets must be added to the Time Sync program to accommodate those networks in a different time zone than the WS.

Other UTC setting locations and what these settings effect

IP level BACnet Device UTC Offset

The UTC offset value on the Time tab of the BACnet Device object is only used when the BACnet time synchronization method is being used to set time. This setting then follows the BACnet specification where it needs to be the negative value of the GMT setting. For example, if the BACnet device is in the GMT+10 time zone, then set this offset to -(10*60) = -600.

Note4: If using the PE program method, the UTC offset value on the Time tab of the BACnet Device object does not change how time is set in the controllers. However, if the UTC offset value on the Time tab of the BACnet Device object is changed, it will change the current time of the controller to coincide with the new time zone until the time is set again in the controller, or the UTC offset value is removed.

UTC offset in controller configuration Time Settings webpage

This doesn’t change how the time of the controller is set. It is used to set the time of sent email messages when using the SMTP option on this controller.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 8219
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore