At times numbered errors pop up in Cyberstation or you may see a numbered error in the Error Listview
Andover Continuum
  • Continuum Cyberstation
  • Windows
Numbered errors appear in Cyberstation or in an Error Listview and an explanation is needed for troubleshooting
With Continuum running and with the focus on the main Continuum screen or Continuum Explorer, press F1 to bring up the help menu
  1. Select index
  2. Type in ‘error’
  3. Select Error Messages, Cyberstation
  4. This displays a list of some of the error messages that may come up in Cyberstation.
This is not a comprehensive list and it doesn’t provide solutions, but gives an initial idea of what is happening for troubleshooting.
Below is the error list that you will find in the Help
OS Error Messages
Error Hex Code Error text
1 0x0001 No message block available
2 0x0002 No message queue available
3 0x0003 Invalid message block
4 0x0004 Invalid message size
5 0x0005 Message is blocked
6 0x0006 Can't deallocate message, it is on a queue
7 0x0008 Invalid message queue
8 0x0008 Invalid message blocking order
9 0x0009 Invalid process ID
10 0x000A Duplicate queue ID
11 0x000B Timed out waiting for message
CPL Error Messages
1024 0x0400 Name has more than 16 characters
1025 0x0401 Comment has more than 132 characters
1026 0x0402 Comment has more than 132 characters
1027 0x0403 Symbol(s) are not from the correct set
1028 0x0404 Field is too long to display
1029 0x0405 Statement or expression is not correct
1030 0x0406 Array is longer than 32,767 entries
1031 0x0407 FOR and NEXT use different index var names
1032 0x0408 GOTO is not allowed inside a loop
1033 0x0409 Fatal, not enough free memory
1034 0x040A Same line name given to more than one line
1035 0x040B No line has this line name
1036 0x040C Same name for more than one local variable
1037 0x040D No item with that name exists
1038 0x040E Cannot define any more local variables
1039 0x040F BREAK or CONTINUE is outside a loop or block
1040 0x0410 Same name or number for more than 1 argument
1041 0x0411 Operation is not available
1042 0x0412 Number is not valid
1043 0x0413 Number cannot be longer than 132 digits
1044 0x0414 Fatal, bad stack address
1045 0x0415 Fatal, illegal stack operation
1046 0x0416 No function with that name exists
1047 0x0417 Attributes do not apply to local variables
1048 0x0418 No quotation marks at end of string
1049 0x0419 Data type is not same as field type
1050 0x041A Data has more chars than field allows
1051 0x041B Record has too many or too few fields
1052 0x041C More records than RECORD statement allows
1053 0x041D Date or time is not valid
1054 0x041E Path name has too many names
1055 0x041F Attribute does not apply to the item type
1056 0x0420 Local variable name cannot be an argument
1057 0x0421 Incorrect array entry type
1058 0x0422 Alarm expression is too long
1059 0x0423 You cannot set that item value
1060 0x0424 You cannot change that attribute value
1061 0x0425 Name is not a program or function name
1062 0x0426 Cannot enable/disable all of one type
1063 0x0427 You must give a name of a local data file
1064 0x0428 Parser stack overflow
1065 0x0429 Cannot use that var as FOR...NEXT index var
1066 0x042A Data file is too long
1067 0x042B You cannot change value of system variable
1068 0x042C Statement is too long
1069 0x042D 0, C or E is a reserved line name
1070 0x042E Feature not available on this controller
1071 0x042F Number must be an integer
1072 0x0430 Passed too many arguments to a function
1073 0x0431 An argument index must be from 1 to 15
1074 0x0432 No chars allowed after continuation symbol
1075 0x0433 Cannot run or stop program from command line
1076 0x0434 Report files are not supported yet
1077 0x0435 Unknown command option
1078 0x0436 Name given is not a controller name
1079 0x0437 Command is valid only from the command line
1080 0x0438 Command is valid only in a program or function
ITP Messages
2048 0x0800 Tried to set item you cannot set
2049 0x0801 Set point or var to value of wrong type
2050 0x0802 Tried to use local var that does not exist
2051 0x0803 An expression uses an operand incorrectly
2052 0x0804 Must set HOUR to value from 0 to 23
2053 0x0805 String is too long
2054 0x0806 Operation is not available
2055 0x0807 Scanner runtime stack overflow
2056 0x0808 Used an incorrect function argument
2057 0x0809 Tried to print to a non-string item
2058 0x080A Tried to rotate prog to nonexistent line
2059 0x080B Used an item type when it is not allowed
2060 0x080C Tried to divide a value by zero
2061 0x080D Gave an array entry that does not exist
2062 0x080E Gave non-numeric var as array index
2063 0x080F Gave more or less arguments than allowed
2064 0x0810 Date or time is not valid
2065 0x0811 Executed too many statements on one line
2066 0x0812 Function did not give the expected result
2067 0x0813 FOR...NEXT loop index variable not numeric
2069 0x0815 Invalid import point address
2070 0x0816 Used name that is not a data file name
2071 0x0817 Used rec or field data file does not have
2072 0x0818 Cannot read data file
2073 0x0819 Cannot write to data file
2074 0x081A Path name is not an actual path
2075 0x081B Attribute does not apply to the item type
2077 0x081D Tried to set attribute to an invalid value
DCP Error Messages
3072 0x0C00 Operation is not available
3073 0x0C01 String is too long
3074 0x0C02 Fatal, not enough free memory
3075 0x0C03 Exceeded number of displayable lines
3076 0x0C04 Invalid import point address
3077 0x0C05 Statement is too long
3078 0x0C06 Controller cannot find an item
3079 0x0C07 Controller cannot open a file of this type
3080 0x0C08 Date or time is not valid
OMS Error Messages
5121 0x01401 Cannot find the item
5122 0x01402 Reached end of the list
5123 0x01403 Attribute does not apply to the item
5124 0x01404 Name is too long
5125 0x01405 Attribute is inappropriate
5126 0x01406 Cannot access file on other controller
5127 0x01407 FatalErr__ Gave invalid hash table size
5128 0x01408 Not enough memory
5129 0x01409 SysErr__ Passed invalid info to database
5130 0x0140A Item is being used and not available now
5131 0x0140B Access to the item denied
5132 0x0140C Array index too large or too small
5133 0x0140D SysErr__ Invalid format for retrieving data
5134 0x0140E Cannot associate these items
5135 0x0140F No relationship of the type defined for item
5136 0x01410 SysErr__ Passed invalid setup to database
5137 0x01411 Reached end of the list of related items
5138 0x01412 Line is too long
5139 0x01413 Value does not apply to the attribute
5140 0x01414 File read error
5141 0x01415 Duplicate item name
5142 0x01416 SysErr__ Cannot set/get attribute
5143 0x01417 SysErr__ Terminal communication error
5144 0x01418 Lbus creation failed
5145 0x01419 String display failed
5146 0x0141A SysErr__ Cannot access the item in database
5147 0x0141B Incorrect path name
5148 0x0141C Incompatible value
5149 0x0141D SysErr__ Invalid message queue Id
5150 0x0141E SysErr__ Session not found
5151 0x0141F Attribute not defined yet
5152 0x01420 Invalid auto-conversion
5153 0x01421 Zero string size
5154 0x01422 Not allowed to delete a system variable
5155 0x01423 SysErr__ System hash tables locked
5156 0x01424 The class object list locked
5157 0x01425 Duplicate handle Id
5158 0x01426 Not enough memory - reset log array size
5159 0x01427 HardwareErr__ Bad RTC chip
5160 0x01428 Duplicate serial number
5161 0x01429 Duplicate Infinet Id number
5162 0x0142A Infinet learn mode is in process
5163 0x0142B Line name is undefined
5164 0x0142C SysErr__ Reserved line label
5165 0x0142D Unable to send the message
5166 0x0142E Dump process stopped
5167 0x0142F Controller not found
5168 0x01430 Invalid handle Id
5169 0x01431 Incorrect line or statement
5170 0x01432 Missing end of controller statement
5171 0x01433 Does not know the type
5172 0x01434 Not allowed to set the attribute
5173 0x01435 Not allowed to set the description
5174 0x01436 Not allowed to set the format
5175 0x01437 Not allowed to set the engineering unit
5176 0x01438 Item already exists
5177 0x01439 Not allowed to set the attribute
5178 0x0143A SysErr__ Invalid controller path
5179 0x0143B SysErr__ Invalid current controller message
5180 0x0143C Invalid response from other controller
5181 0x0143D Item is already being used
5182 0x0143E File is being saved by another operator
5183 0x0143F File is too long
5184 0x01440 Cannot access the item on other controller
5185 0x01441 SysErr__ Passed invalid indicator to database
5186 0x01442 Invalid Energynet ID
5187 0x01443 Invalid Infinet ID
5188 0x01444 Invalid Infinet port
5189 0x01445 Missing end of dictionary statement
5190 0x01446 Missing end of import/export statement
5191 0x01447 Unable to compile the file
5192 0x01448 Invalid dump file statement
5193 0x01449 Missing end of block statement
5194 0x0144A Missing end of code statement
5195 0x0144B Missing end of object statement
5196 0x0144C Unable to rename the controller
5197 0x0144D Unable to rename the comm port
5198 0x0144E Item has no type
5199 0x0144F Undefined alarm
5200 0x01450 Attribute can only be retrieved, not set
5201 0x01451 Conversion too long
5202 0x01452 Not allowed to retrieve the attribute value
5203 0x01453 No default format defined
5204 0x01454 SysErr__ Passed invalid indicator to database
5205 0x01455 Invalid schedule type
5206 0x01456 Missing colon in the statement
5207 0x01457 Incorrect name
5208 0x01458 Incorrect header for the code block
5209 0x01459 Incorrect header for a sub block
5210 0x0145A Incorrect header for the object block
5211 0x0145B Undefined system variable
5212 0x0145C Undefined comm port
5213 0x0145D Not allowed to create an alarm
5214 0x0145E Inappropriate request for the comm port
5215 0x0145F Invalid mode for the comm port
5216 0x01460 LBus is already set up
5217 0x01461 Invalid program file
5218 0x01462 Program is already in the firing order
5219 0x01463 Unable to access the item
5220 0x01464 No response to the Infinet token pass
5221 0x01465 NetworkErr__ Received incorrect CRC on Infinet
5222 0x01466 SysErr__ Invalid error value from Infinet
5223 0x01467 Attribute does not apply to the point type
5224 0x01468 Attribute does not apply to the port type
5225 0x01469 Item must be a program
5226 0x0146A File must be open
5227 0x0146B File took too long to open
5228 0x0146C Cannot alter the file
5229 0x0146D Cannot add or remove records
5230 0x0146E The relationship is already set up
5231 0x0146F CAnnot dump dictionary block of controller
5232 0x01470 Cannot dump the controller
5233 0x01471 Cannot dump associated items
5234 0x01472 Undefined IOU number
5235 0x01473 Invalid channel number
5236 0x01474 No free alarm links
5237 0x01475 Cannot access next Enet controller in list
5238 0x01476 Cannot access next Infinet controller in list
5239 0x01477 Incorrect header for the log array block
5240 0x01478 Invalid log array index
5241 0x01479 Cannot modify the file
5242 0x0147A Unable to create the Infinet controller
5243 0x0147B Zero is not a valid serial number
5244 0x0147C Invalid baud rate
5245 0x0147D Comm port is not set up for Infinet
5246 0x0147E Controller is not online
5247 0x0147F Not allowed to delete a comm port
5248 0x01480 Cannot define any more handle IDs
5249 0x01481 Invalid controller name
5250 0x01482 Invalid Infinet controller name
5251 0x01483 Invalid Energynet controller network ID
5252 0x01484 Controller doesn't know Infinet ID
5253 0x01485 Invalid electrical type
5254 0x01486 Invalid DateTime value
5255 0x01487 Invalid log type
5256 0x01488 Invalid floating point number
5257 0x01489 Attribute doesn't exist for the item
5258 0x0148A Access to the conversion denied
5259 0x0148B Number of array entries is too  arge
5260 0x0148C Invalid program status
5261 0x0148D Unable to access the comm port
5262 0x0148E Cannot overwrite the item
5263 0x0148F New default mode is current mode
5264 0x01490 Cannot set export flag for Enet controller
5265 0x01491 Operation is not supported
5266 0x01492 SysErr__ Unused sched events are inaccessible
5267 0x01493 Sched occup/unoccup variable not DateTime
5268 0x01494 Holiday schedule doesn't exist
5269 0x01495 Import/Export item must be a point
5270 0x01496 Point must export to controller/alarm
5271 0x01497 Sched occupancy flag not output/numeric point
5272 0x01498 Item is not a holiday schedule
5273 0x01499 Cannot dump the import/export block
5274 0x0149A Cannot set up the port
5275 0x0149B Index number for the alarm is too large
5276 0x0149C Invalid state
5277 0x0149D Comm port is busy
5278 0x0149E Reference array is full
5279 0x0149F Undefined alarm type
5280 0x014A0 Item is not local controller
5281 0x014A1 HardwreErr__ Bad EEPROM chip
5282 0x014A2 Cannot retrieve controller model number
5283 0x014A3 Cannot retrieve controller serial number
5284 0x014A4 Unspecified Enet ID
5285 0x014A5 Undefined controller model number
5286 0x014A6 Controller has no assigned Infinet port
5287 0x014A7 Cannot find controller in the Infinet list
5288 0x014A8 Invalid password
5289 0x014A9 Cannot retrieve controller version number
5290 0x014AA Handle ID is out of range
5291 0x014AB Not allowed to delete user ACC
5292 0x014AC Not allowed to use this many Infinet devices
5293 0x014AD Not allowed to change user ACC's security level
5294 0x014AE Full path is not set
5295 0x014AF Access denied
5296 0x014B0 User passwords are mismatched
5297 0x014B1 User doesn't exist on remote controller
5298 0x014B2 Invalid stop bits
5299 0x014B3 Invalid data length
5300 0x014B4 The user is logged in
5301 0x014B5 Not allowed to change user name
5302 0x014B6 Not allowed to delete this controller
5303 0x014B7 No TankProbe extension block installed
5304 0x014B8 No TankNet exists
5305 0x014B9 TankNet is already set up
5306 0x014BA Can't change a TankProbe to another electrical type
5307 0x014BB Duplicate PIN
5308 0x014BC There is no card information available for this person
5309 0x014BD Invalid card entry
5310 0x014BE Duplicate card
5311 0x014BF Invalid schedule
5312 0x014C0 Attribute does not apply to object type
5313 0x014C1 Undefined card type
5314 0x014C2 Invalid PIN value
5315 0x014C3 Same area on both sides of a door is not allowed
5316 0x014C4 The maximum number of doors allowed has been reached
5317 0x014C5 Personnel cleanup in progress.  Please try again.
5318 0x014C6 Unable to delete one or more personnel objects on rip
5319 0x014C7 Personnel distribution in process.  Please try again.
5320 0x014C8 Not allowed to set an area in a DefaultDoor
5321 0x014C9 Unable to set remote sync bit for one or more personnel objects
5322 0x014CA Could not synchronize CX and SX databases
5327 0x014CF Event log size has been automatically adjusted
5328 0x014D0 No XDriver code module installed
5329 0x014D1 XDriver code module installed
5330 0x014D2 XDriver code module incomplete
5331 0x014D3 Checksum error detected in S-record
5334 0x014D6 Duplicate XDriver parameter
5338 0x014DA Invalid IP parameter
5339 0x014DB Invalid Subnet Mask for the IP class
5340 0x014DC IP network number should not equal 0
5341 0x014DD IP host number should not be all 1s
5342 0x014DE Possible Infinet bus short detected
5345 0x014E1 Update operation still in progress
5348 0x014E4 Invalid NetWare frame type
5349 0x014E5 UTC Offset is out of range
5350 0x014E6 No personnel cache entries available
5351 0x014E7 Memory expansion board not installed
5352 0x014E8 Flash memory operation failure
5353 0x014E9 Too many IOUs
5354 0x014EA The maximum number of areas allowed has been reached
5355 0x014EB Attempt to lock door has failed
5356 0x014EC Attempt to unlock door has failed
5357 0x014ED OMS database has become corrupt
5358 0x014EE OMS internal error
5359 0x014EF Buffer too small for data requested
5360 0x014F0 OMS database not currently available (backing up)
5361 0x014F1 String size exceeds implementation limit
5362 0x014F2 Backup disabled due to excessive use (requires manual enable)
5363 0x014F3 Schedule events are out of order
5364 0x014F4 Invalid bookmark for error log
5365 0x014F5 Duplicate SmartSensor control point
5366 0x014F6 Inappropriate value for current restart mode
5367 0x014F7 Copy protection violation has occurred —  please contact your ACC dealer
5368 0x014F8 Error sending CustomABAFormat string to IOU module
5369 0x014F9 OBJ_ERR_BACnet_ERROR  - A BACnet error occurred.
5370 0x014FA OBJ_ERR_DABL_OVERFLOW - The controller has reached its BACnet device binding limit.
LAN Error Messages
6144 0x1800 Comm user return
6145 0x1801 Comm invalid message length
6146 0x1802 Comm invalid destination address
6147 0x1803 Comm invalid source address
6148 0x1804 Comm invalid QID
6149 0x1805 The port is not an Infinet
6150 0x1806 The controller is not responding
6151 0x1807 Comm LAN reconfig in progress
6152 0x1808 The controller is offline
6153 0x1809 The EnergyNet is not configured
6154 0x180A Comm destination node paused
6155 0x180B Send request timeout
6156 0x180C Send error
6157 0x180D NULL message received
6158 0x180E Unable to send message
6159 0x180F Invalid EnergyNet node ID
6160 0x1810 Duplicate Ethernet ID
6161 0x1811 Duplicate EnergyNet ID
6162 0x1812 Out of memory
6163 0x1813 Ethernet RAM test faillure
6164 0x1814 Undefined EnergyNet ID
6165 0x1815 Undefined Ethernet ID
GLB Error Messages
7169 0x1C01 Symbol name too long
7170 0x1C02 Invalid characters in symbol
7171 0x1C03 Symbol cannot be a system variable
7172 0x1C04 No items
7173 0x1C05 Too many items
7174 0x1C06 First character must be alpha
7175 0x1C07 System internal error
7176 0x1C08 System clock was changed
IES Error Messages
8192 0x2000 Cannot build IE API request
8193 0x2001 Cannot send IE API request
8194 0x2002 IES has bad OMS pointer
8195 0x2003 IE handle points to wrong network address
8196 0x2004 IE handle is invalid
8197 0x2005 IE bad data in ObjKey
8198 0x2006 IE API response not received
8199 0x2007 IE no Infinet
8200 0x2008 Could not establish import
8201 0x2009 IE database locked
LBS Error Messages
9217 0x2401 LBus not ready
9218 0x2402 wait_collect or wait_update timeout
9219 0x2403 Invalid IOU number
9220 0x2404 LBus database is locked
9221 0x2405 An active IOU exists
9222 0x2406 LBus error no memory
9223 0x2407 Comm channel specified is invalid
9224 0x2408 Sensor's channel is invalid
9225 0x2409 LBus does not exist
9226 0x240A The IOU number has not been defined yet
9227 0x240B Bad electrical type
9228 0x240C Value is too large or too small
9229 0x240D IOU communication status = online
9230 0x240E IOU communication status = offline
9231 0x240F IOU number is not between 1 and 16
IOS Error Messages
10240 0x2800 NULL
10241 0x2801 Type not valid for this IO channel
10242 0x2802 IO channel number out of range
10243 0x2803 IO channel already assigned
10244 0x2804 Vref out of tolerance
10245 0x2805 IO channel is unassigned
10246 0x2806 Tri-state partner is already assigned
10247 0x2807 AD converter trashed
10248 0x2808 AD converter timed out
10249 0x2809 Reference channels not initialized
10250 0x280A Adjacent channel is already in use
10251 0x280B Invalid channel for RTD use
10252 0x280C Cannot delete IOU module until all associated objects are moved to other IOU modules or deleted
10253 0x280D Duplicate module ID
10254 0x280E Insufficient memory for IO operation
10255 0x280F IO module is not commissioned
10256 0x2810 Incorrect channel type
10257 0x2811 Channel doesn't exist
10258 0x2812 Error installing IO system
10259 0x2813 Error in IO database
10260 0x2814 Module is not saved
10261 0x2815 Attribute does not exist
10262 0x2816 IO message queue does not exist
10263 0x2817 Illegal IO queue designator
10264 0x2818 IO module number is too large
10265 0x2819 IO queue is full
10266 0x281A No IO message buffers available
10267 0x281B Unknown IO message buffer size
10268 0x281C IO routing table section doesn't exist
10269 0x281D IO routing table entry not saved
10270 0x281E IO module response was lost
10271 0x281F IO MIP interface initialization error
10272 0x2820 No response from IO module
10273 0x2821 Illegal message received from IO module
10274 0x2822 IO module message data error
10275 0x2823 IO module message is not a service pin message
10276 0x2824 No IDs available for IO module commissioning
10277 0x2825 Too many IO modules for the controller
10278 0x2826 IO module domain update error
10279 0x2827 IO module read memory command failed
10280 0x2828 IO module update address command failed
10281 0x2829 IO module update NV cnfg table failed
10282 0x282A No message tags available for IO message
10283 0x282B Not a suitable replacement IO module
10284 0x282C Error in routing IO module response
10285 0x282D Incorrect response from IO module
INF Error Messages
11264 0x2C00 NULL
11265 0x2C01 Comm port cannot connect an Infinet
11266 0x2C02 Comm port already set up for another purpose
11267 0x2C03 Comm port has not been assigned a purpose
11268 0x2C04 No Infinet controller with that serial number
11269 0x2C05 Infinet is not set up
11270 0x2C06 Infinet ID is already in use
11271 0x2C07 ID is not valid for Infinet
11272 0x2C08 Message received is not for an Infinet controller
11273 0x2C09 Controller received message from an unknown source
11274 0x2C0A Learn mode currently in use
11277 0x2C0D Learn already in process on this port
11280 0x2C10 Infinet controller is not responding
11281 0x2C11 NULL buffer passed to Infinet server
11282 0x2C12 Message type is not supported by Infinet server
I2LD Error Messages
202752 0x31800 No model matching download header exists on this CX
202753 0x31801 Error found in I2 download header
202754 0x31802 Error found in I2 model information
202755 0x31803 Models in I2 download exceeds maximum
202756 0x31804 Received download message type out-of-service
202757 0x31805 Begin I2 download header not received
202758 0x31806 Comm Error - socket receive
202759 0x31807 Comm Error - socket send
202760 0x31808 No comm buffers available
202761 0x31809 Download state machine error
202762 0x3180A Illegal message type response from Infinet controller
202763 0x3180B Listen call failed
202764 0x3180C Bind call failed
202765 0x3180D Socket call failed
202766 0x3180E Received short packet - not enough data
202767 0x3180F Application type unknown by I2
202768 0x31810 Download model does not match I2 model
202769 0x31811 Unknown/unsupported message type
202770 0x31812 I2 download out-of-sync
202771 0x31813 I2 received unknown/unsupported packet type
202772 0x31814 I2 received segment that exceeds block storage
202773 0x31815 I2 received block address out-of-range for flash
202774 0x31816 I2 detected end of download CRC error
202775 0x31817 I2 does not support download revision
202776 0x31818 I2 is running in boot loader mode
202777 0x31819 I2 total received block count does not match
202778 0x381A I2 detected external RAM failure
202779 0x3181B I2 malloc failure during boot-up
202780 0x3181C I2 detected unknown flash device