Gather Continuum Controller error logs if requested by Product Support for troubleshooting

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Gather Continuum Controller error logs if requested by Product Support for troubleshooting
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • Chris_Asbury
    Chris_Asbury
  • Alan_Wood
    Alan_Wood
  • JohnBoehmer
    JohnBoehmer

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
5155 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Gather Continuum Controller error logs if requested by Product Support for troubleshooting

Picard Product_Support
‎2018-09-07 01:32 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:16 AM

Issue

Controller Error Logs - How to gather Continuum Controller error logs if requested by Product Support for troubleshooting.

Product Line

Andover Continuum

Environment

  • BCX
  • CX 
  • CMX
  • 9680
  • 9900
  • i2
  • b3
  • 9702
  • Controller Error Log
  • Gerry Log

Cause

Troubleshooting controllers often time requires obtaining an error log from the controller

Resolution

The controller error logs contain useful diagnostic information when it is necessary to troubleshoot a controller or system problem. Much of what is logged are normal system operations that may assist an engineer in diagnosing a problem in the field.

To get the error logs from various controllers follow the procedures below:

NetControllers - 99xx 

  • Dumb terminal in using HyperTerminal
  • Sign into the NetController
  • Press V then E and press Enter over the NetController you are attached to
  • Press F2
  • Hit Alt + Print screen and paste into a Word doc
  • Arrow down to single space or Ctrl+D to page down
  • Hit Alt + Print screen and paste into a Word doc
  • Repeat this process until you are at the end of the errors (up to 200)
  • F4 Exits the error log
  • See the CX Controllers Programmer’s Guide for all terminal keystrokes
  • Email the file to Product Support Services
     

BCX/i2/B3 Controllers

CX9680/ACX5720/ACX5740/9702 Controllers

Note: You can not retrieve errors from NetController I (CX9900) using this tool

  • Controller Error Log Tool
  • Navigate to C:\Program Files\Continuum
  • Double click on ControllerErrorLogTool.exe to open (This will do an install the first time)
  • Note: The ErrorLogTool.exe is an older version of this utility and will work, but gives less information and does not contain the error lookup feature.
  • Enter in the BCX or master CX IP
  • Transport type = UDP or TCP depending on controller configuration
  • CX Enode ID = AccNetId from the main CX editor
  • Select Continuum in the Mode area, top right

If the controller is a field device then enter the following:

  • CX infinet port = Select the one you want to report on
  • Infinet Node ID = port number of the i2 device you want the error log out of

Once all the above required entries have been made:

  • Click Get Log and the page will populate with any errors
  • Once this runs, select SaveAs and name the file
  • Email the file to Product Support Services

Suppliment - To gather error logs from Continuum controllers transisioned to StuxureWare please see How to pull the error log from a b3 or Infinet controller in SmartStruxure.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2786
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore