BACnet bCX MSTP network loses communication when a b-Link is added or removed
  • BACnet bCX MSTP network loses communication when a b-Link is added or removed
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • PaulFr
    PaulFr
  • Alan_Wood
    Alan_Wood
  • Dave_Shore
    Dave_Shore
‎2018-09-11 05:54 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:19 PM
Andover Continuum
MSTP b3 bCX4040  b-Link
The bCX MSTP circuitry is slightly different to the b-Link  MSTP circuitry , thus under some circumstances, other faults on the MSTP network can cause communication to change, when the network is connected via a b-Link
  1. If an MSTP network is installed correctly, then it will operate correctly at all speeds up to 76.8k (assuming all devices operated up to this speed)
  2. If the MSTP network is not stable up to 76.8k, or adding or removing a b-Link causing a loss of communication, then it is likely there is some fault on the network.
    (adding or removing the end of line termination resistors, is also a useful fault finding option)
  3. The bCX MSTP components are slightly different to the b-Link MSTP components, thus under some circumstances, other faults on the MSTP network can cause communication to be lost, when the network is connected via a b-Link
Example
This has been seen when third party variable speed drives (VSDs) were connected to a bCX MSTP network (these unit had switchable termination resistors that by default were in circuit)
The communication was ok at a low speed (19200) connected directly to a bCX, but when the network was put on the secondary side of a b-Link, the communication failed.
Once the termination resistors were switched out of circuit, the communication via the b-Link was fine.
In the example above the VSDs were by ABB
Related: How to change the Baud Rate of a field bus (Infinet or Bacnet MSTP) when there is an Infilink or B-l...
Tags (2)
  • 13759