How to Import a Large Number of Individuals from Excel to I/NET SQL Database at One Time

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to Import a Large Number of Individuals from Excel to I/NET SQL Database at One Time
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • sesa145087_brid
    sesa145087_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
698 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to Import a Large Number of Individuals from Excel to I/NET SQL Database at One Time

Picard Product_Support
‎2018-09-11 06:29 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 07:31 PM

Issue

In some projects there is demand for importing a large number of individuals from an existing spreadsheet for individual information at one time.

Product Line

TAC INET

Environment

  • I/NET Seven Revision 2.xx and higher
  • Microsoft SQL Server Management Studio Express

Cause

In some cases the customers have a spreadsheet or database of employees and/or users which they want to quickly import into their I/NET Seven Access control database.

Resolution

The whole process is to import the data from the excel file to the IDWorksView table of SQL database of I/NET. The steps below needs to be followed:


  1. Prepare the Microsoft SQL Server Management Studio Express. Click here to down this tool for version 2005 free of charge. If for version 2008, click here to download. Then install this tool.
  2. Download the individual spreadsheet Excel template and SQL script here. Save to the C:\.
  3. Ensure that the Tenant, Group have been added in I/NET already. Also ensure that all the card numbers in the spreadsheet don't conflict the ones already in I/NET.
  4. Enter the individual information into this template. If there are photos for individuals, the folder of the photos also need to be entered.
  5. Open the Microsoft SQL Server Management Studio Express and connect to the database.
  6. Find the InetDb database, and open the SQL script just downloaded from the File menu.
  7. Click Execute to run the script. Then if without any problems, the successful result will be shown in the output message window.
  8. The next step is to get the imported data downloaded to the controllers.
    • For each SLI perform a station SAV and station restore – it may take some time for all this information to be downloaded to the DPUs and may fail in some instances.  You may also notice the system slow up for some time (hours) until all of this information has been successfully downloaded to the controllers. 
    • It may also be necessary to force the data into the DPU by performing staggered DPU Restores on specific doors that are experiencing incorrect functionality. 
  9. There is also a method that download the imported data without any operation in I/NET software by a function called Automatic DPU Restore. Refer to Automatic DPU Restore and Individuals added via Datacard ID Works are not getting access to doors for detailed information about how to set Automatic DPU Restore in I/NET.

This is the method using SQL Server Management Studio Express. The Microsoft Access can also be used to do the importing work. Refer to How to import a large number of Individuals into an I/NET Access Control database for detailed information.

Labels (1)
Labels:
  • TAC INET
Attachments
IDWorksview Import_New.zip
Tags (3)
  • Find more articles tagged with:
  • 8386
  • Datacard
  • ID Works
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore