EPU305LCD - suggested maximum length on measurement hose?
Hello there,
A consultant reaching out with a question, what is the suggested maximum length of tubing/hose used for differential pressure measurement? Commercial Reference: EPU305LCD
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-2606:18 AM
Discussed internally and got following feedback:
Its a "rule of thumb" recommendation not based any testing of this.
The general guidance is to keep the runs of tubing as short as possible to maintain accuracy and response time. I would recommend tubing no longer than 100 ft for best performance.
However, if longer distances are required, the customer should validate the performance of a single unit prior to committing to a full build.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-2606:18 AM
Discussed internally and got following feedback:
Its a "rule of thumb" recommendation not based any testing of this.
The general guidance is to keep the runs of tubing as short as possible to maintain accuracy and response time. I would recommend tubing no longer than 100 ft for best performance.
However, if longer distances are required, the customer should validate the performance of a single unit prior to committing to a full build.