NMC user configuration in IT Expert

Device configuration

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Expert
  • Configuration
  • Device configuration
  • NMC user configuration in IT Expert
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Video: Device configuration
  • Device configuration - Gateway versions 1.24 and o...
  • NMC user configuration in IT Expert
  • Video: Device configuration
  • Device configuration - Gateway versions 1.24 and o...
  • NMC user configuration in IT Expert

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Device configuration
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
4583 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

NMC user configuration in IT Expert

Sisko JLehr Sisko
‎2024-09-24 06:45 AM

In this article

 

  • Overview
  • Create or modify users
  • Modify super user
  • Modify default user settings
  • Delete users
  • Common reasons for configuration failures

 

Overview

 

In IT Expert, go to Device configuration > User configuration to create, modify, or delete users on selected APC NMC 2 and NMC 3 devices with APC AOS v6.x or later (excluding v6.0.6-6.1.1).

Need NMC help?

 

Only supported NMC 2 and NMC3 devices in your organization are available to configure.

 

It is recommended that you enable strong passwords. If you enable strong passwords, new passwords created for user accounts require:

 

  • A minimum of 8 and maximum of 64 characters
  • Not found in a list of 5000 known compromised passwords

    NMC 3 Security Handbook

 

It is required that all the Gateways in your organization to be updated to version 1.23 or newer.

If a device is monitored by multiple Gateways, one of the Gateways is automatically selected to apply the configuration change.

All Gateways monitoring a device should be properly configured with file transfer credentials to reduce the risk of failure.

 

IMPORTANT: User credentials are also configured in the Gateway for device communication. Changes made to these user credentials in IT Expert must also be made in the Gateway, and the devices must be rediscovered.

Otherwise, communication with the Gateway will be lost. 

Configure APC NMC device credentials in the Gateway

Configure Gateway device file transfer settings

 

You can modify user configurations on up to 500 devices at a time.

 

NMC 3 devices can accept no more than 11 parameters for each device including the username and password.

 

idea_icon.png  Choose only a few devices to test the configuration before you update all your devices.

 

User configuration options are different for each action:

 

  • Create or modify users
  • Modify super user
  • Modify default user settings
  • Delete users

 

ITE user configuration overview page 1a.png

 

 

Create or modify users

Log out of any devices where you are modifying the user configuration.

 

1. Select devices

 

Select the devices where you want to create or modify user configurations.

Filter the list by location, model, or device as needed.

 

ITE user config modify user.png

2. Configure users

 

Check the box ITE user configuration acknowledgement checkbox.png to acknowledge that user settings you modify using IT Expert may also need to be modified in the Gateway. 

Note: You cannot proceed until you acknowledge you understand that additional configuration in the Gateway may be required.

 

Click Add user entry to create the list of users you want to create or modify.

Username and password fields are required for every entry.

 

Depending on the devices you select, a new user might be created on some devices and existing users might be updated on others.


If the username you enter already exists on the device, the password you specify and any custom options will be updated.


If the username you enter does not exist on the device, a new user will be created with the specified username and password and any custom options.

 

Click the settings icon in each entry ITE user configuration settings icon.png to customize the user settings. 

 

When you update an existing user, Using default options means the existing settings for the user will not be modified on the device.

 

When you create a new user, Using default options means the default user options defined by the device are used.

 

Toggle the button next to each custom option modify it.

 

ITE user configuration configure user 1.png

 

Any options not defined in Customize user settings use the device's default options for the user.

 

Custom options that can be modified using IT Expert include:

 

User settings

  • Enable/disable user
  • Role: Administrator. Device, Network only, Read only

    Note: You cannot create or modify Outlet role users on rPDUs that support it. You must configure the Outlet role directly on the device.

  • Description: Modify the existing description, or leave blank to remove the existing description.

 

Security settings

  • Session timeout (1-60 minutes)
  • Serial remote authentication override: Disabled/Enabled

 

Display settings

  • Units: Metric, US Customary
  • Date format
  • Language: The language setting will not take effect if the language you choose is not installed on the destination device.

 

Log settings

  • Event log color coding: Disabled/Enabled
  • Log export format: CVS/Tab

 

3. Confirm and apply

 

Show or hide the list of devices affected by user configuration changes.

Click Apply to send the user configuration to the devices.

 

ITE user configuration apply settings show device list 1.png

 

 

Modify super user

Log out of any devices where you are modifying the user configuration.

 

The apc super user is the system admin user.  You cannot change the username, change the role, or delete this user.

 

1. Select devices

 

Select the devices where you want to modify the super user configuration.

Filter the list by location, model, or device as needed.

 

ITE user configuration delete user.png

 

2. Modify super user

 

Check the box ITE user configuration acknowledgement checkbox.png to acknowledge that user settings you modify using IT Expert may also need to be modified in the Gateway.

Note: You cannot proceed until you acknowledge you understand that additional configuration in the Gateway may be required.

 

The current password for the apc super user is required to modify the settings.

 

Toggle the button next to each custom option modify it.

 

ITE user configuration configure super user.png

 

Options that can be modified using IT Expert include:

 

User settings

  • New password
  • Enable user
  • Description: Modify the existing description, or leave blank to remove the existing description.

 

Security settings

  • Session timeout (1-60 minutes)
  • Serial remote authentication override: Disabled/Enabled

 

Display settings

  • Units: Metric, US Customary
  • Date format
  • Language: The language setting will not take effect if the language you choose is not installed on the destination device.

 

Log settings

  • Event log color coding: Disabled/Enabled
  • Log export format: CVS

 

3. Confirm and apply

 

Show or hide the list of devices affected by user configuration changes.

Click Apply to send the user configuration to the devices.

 

ITE user configuration apply settings show device list super user 1b.png

 

 

Modify default user settings

Log out of any devices where you are modifying the user configuration.

 

1. Select devices

 

Select the devices where you want to modify the default user configuration.

Filter the list by location, model, or device as needed.

 

ITE user config modify default user.png

 

2. Modify default user

 

Configure settings applied when new users are created.

Note: Settings modified in IT Expert are not retroactively applied to existing users.

 

Toggle the button next to each custom option modify it.

 

ITE user configuration configure default user.png

 

Any options not defined in Customize user settings use the device's default options for the user.

 

Custom options that can be modified using IT Expert include:

 

User settings

 

  • Enable/disable user
  • Role: Administrator. Device, Network only, Read only
  • Description: Modify the existing description, or leave blank to remove the existing description.

 

Note: You cannot create or modify Outlet role users on devices that support it. You must configure the Outlet role directly on the device.

 

Security settings

  • Require strong passwords 
  • Require password change (0-365 days, 0 = Disabled)
  • Session timeout (1-60 minutes)
  • Serial remote authentication override: Disabled/Enabled

 

Display settings

  • Units: Metric, US Customary
  • Date format
  • Language: The language setting will not take effect if the language you choose is not installed on the destination device.

 

Log settings

  • Event log color coding: Disabled/Enabled
  • Log export format: CVS/Tab

 

3. Confirm and apply

 

Show or hide the list of devices affected by user configuration changes. Click Apply settings.

 

ITE user configuration apply settings show device list default user 1a.png

 

 

Delete users

Log out of any devices where you are modifying the user configuration.

 

1. Select devices

 

Select the devices where you want to modify the super user configuration.

Filter the list by location, model, or device as needed.

 

ITE user configuration delete user.png

 

2. Delete users

 

Check the box ITE user configuration acknowledgement checkbox.png to acknowledge that user settings you modify using IT Expert may also need to be modified in the Gateway.

Note: You cannot proceed until you acknowledge you understand that additional configuration in the Gateway may be required.

 

Click Add user entry to create the list of users you want to delete.

 

If the username you enter exists on the device, the user will be deleted.

 

ITE user config modify delete user.png

 

3. Confirm and apply

 

Show or hide the list of devices affected by user configuration changes. Click Apply settings.

 

ITE user configuration apply settings show device list delete user.png

 

View progress and results

 

Results are listed on the User configuration main page including the configuration action, the IT Expert user who initiated the action, the time the action occurred, the number of devices affected, any ongoing progress, and final results.

 

Click the link in the Devices column to see results listed by device:

 

  • Complete: The configuration was sent to all devices successfully.
  • Partial: The configuration was sent to some devices.
  • Failure: The configuration was not sent to any devices.

 

Check the device's event log for more details about configuration changes.

 

ITE user configuration overview page with results 1.png

 

Common reasons for failures

 

IT Expert - Device communication failure

 

IT Expert - Device not recognized

 

IT Expert - Device is offline

 

 

 

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore