Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Use this portal to submit your innovative ideas to make Geo SCADA Expert and Devices such as SCADAPack, Trio and Realflo of greater value to you and to the SCADA & Telemetry community. Every idea will be individually reviewed by our team for merit and will be marked Under Consideration.
Search in
I was reminded of this issue that I've run into a couple of times with Geo SCADA Expert and certain Modbus devices.
The best example is when using a Rockwell ControlLogix with a 1756-EN2T (for example). It's possible to write some custom logic to handle Modbus transactions. However, there are data size restrictions on the raw socket comms, which means that full length ModbusTCP packets can't be used.
I've gotten around this in the past by deliberately keeping gaps in my Modbus register map, so that Geo SCADA Expert won't try to consolidate a whole set of adjacent reads into one long multiple register read (ditto for writes).
However, it would be nicer if the Modbus data map could remain 'perfect' and the limitation on transfer lengths could just be configured in Geo SCADA Expert (i.e. the ControlLogix Modbus implementation can only handle a maximum of 120 registers in one request).
Limitations from the ControlLogix ModbusTCP shown below