ViewX asks the server what port to use when the script engine initializes i.e. when a mimic is opened. Each mimic has its own instance of the script engine. If the port is changed on the server, mimics that are currently open on clients will stop working. If the web server is not running (due to port clash with other web services on the server), client side scripting won't work.
This page shows some errors associated with the issue. Please also follow this link for more details: Diagnosing Scripting Connection Errors
script_failure.png
Error message "Unknown Error 0x80072efd"
servernotfound.png
Error message "404 Not Found"
or
Error message "405 Method not allowed"
or
"Permission Denied" (if another instance of SCX was running on the port instead)
If you have a proxy defined in your IE configuration, ViewX will try to use that to talk to the web server. This may not be what you want and depending on your setup it wont work (usually the Unknown Error message). Add exclusions in IE for the Geo SCADA servers if you need the proxy set up.