Control Failed Alarm not Clearing until Successful Control Action
Geo SCADA Knowledge Base
Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for
Show only
|
Search instead for
Did you mean:
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
📖HomeBack The "Control action request failed - No reply received from outstation" alarms will stay active until a successful control on that point has been performed.
If you wish to clear the alarm before a successful control takes place, you could use the Remove Alarm option (assuming this option has been enabled by the System Administrator) available by right clicking on the alarm in either the alarm banner or alarm list. Remove Alarm clears an alarm from the alarm lists, even though the alarm condition may still be active. For it to reappear in the alarm list, the alarm condition would need to clear and then become active again for a new alarm to be raised and for this reason its use should be considered very carefully.