Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Configuring Database Aggregates Using DATABASE OBJECT

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • Configuring Database Aggregates Using DATABASE OBJECT
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 04:03 PM
0 Likes
0
1414
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 04:03 PM

Configuring Database Aggregates Using DATABASE OBJECT

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 10, 2021 01:03 AM

📖 Home  Back  
The DATABASE_OBJECT structure does not allow calling methods or writing to properties of aggregates using Logic. However there is a way that this can be done using two structured text programs. The example code below writes to the ControlMinimum and ControlMaximum properties of all Modbus analog points within a group.

Program 1

The first program, uses DATABASE_OBJECT to get the list of points to operate on. This program can update any of the properties of these points in the class defined by DATABASE_OBJECT, for example, ZeroScale and FullScale. The SQL and DATABASE_OBJECT should also return the FullName property from the class. It accepts an input variable that determines which group it should search in the SQL query. The program uses two Double variables to set the ZeroScale and FullScale named "Range Max" and "Range Min".

As part of the processing of each point, call a second ST program (in the example this is called Sub and is in the same directory as the first program) and pass in the object FullName as an input variable.

Note that both ST programs should be set to "On Interval" with an interval of 0.

 

TYPE
ModbusAlgTagName : DATABASE_OBJECT(CModbusPointAlg)
FullScale : INT;
ZeroScale : INT;
FullName : STRING;
END_DATABASE_OBJECT;
END_TYPE

PROGRAM ConfigurePoints

VAR_INPUT
sGroupFullName : STRING;
END_VAR

METHOD
CallSub AT %M(.Sub.Execute) : STRING;
END_METHOD

VAR
ModbusAlgTags AT %S(SELECT Id, Units, FullScale, ZeroScale, TrendMaximum, TrendMinimum, FullName FROM CModbusPointAlg WHERE FullName LIKE ? || '%') : RESULTSET OF ModbusAlgTagName WITH_PARAMS sGroupFullName;
END_VAR

VAR
iRangeMax AT %I(.Range Max) : INT;
iRangeMin AT %I(.Range Min) : INT;
END_VAR

WHILE ModbusAlgTags.Valid DO
ModbusAlgTags.Value.FullScale := iRangeMax;
ModbusAlgTags.Value.ZeroScale := iRangeMin;
CallSub(ModbusAlgTags.Value.FullName);
ModbusAlgTags.Next();
END_WHILE;

END_PROGRAM

 

Program 2

The second program creates read/write variables that point at the required properties, generating the variable using the FullName which is passed in in the VAR_INPUT block.

Note that we have checked whether or not the Control aggregate is enabled first by checking the $Enabled property to avoid errors when attempting to write to properties on an aggregate that is not enabled.

PROGRAM Sub 

VAR_INPUT
FullName : STRING;
END_VAR

VAR
CtrlMax AT %M({FullName}.Control.ControlMaximum) : INT;
CtrlMin AT %M({FullName}.Control.ControlMinimum) : INT;
Enabled AT %M({FullName}.Control.$Enabled) : BOOL;
END_VAR

VAR
iRangeMax AT %I(.Range Max) : INT;
iRangeMin AT %I(.Range Min) : INT;
END_VAR

IF Enabled THEN
CtrlMax := iRangeMax;
CtrlMin := iRangeMin;
END_IF;

END_PROGRAM


Go: Home Back

Labels:
  • database

  • IEC 61131-3 Logic

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore