Time Synchronisation

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • Time Synchronisation
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 04:04 PM
0 Likes
0
2443
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 04:04 PM

Time Synchronisation

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 10, 2021 01:04 AM

📖 Home  Back  

Purpose

Geo SCADA uses external applications for time synchronisation to ensure:

  • All Geo SCADA servers are using the same time, providing accurate data readings and correlation of logging

 

  • Where the protocol supports the functionality, ensuring the remote devices' clocks are correct for timestamped data

For more information on what happens when the clocks drift between Geo SCADA servers refer to Effects of Considerable Server Time Changes, Setting System Clock Backwards Causes Logic to Stop Executing and Effects of RTU Clock Changes on Kingfisher Driver.

Ideally Geo SCADA servers should be in sync within a few milliseconds to avoid any problems. The same is true for the other components of the SCADA system for example client workstations, switches, firewalls and IDS/IPS devices.

Keeping Time in Sync

Windows comes with an inbuilt time service, w32time, which is used to keep a workstation and domain member server's time in sync with a domain controller, or if the workstation or server are not in a domain with an external general time source. However, as documented at http://support.microsoft.com/en-us/kb/939322, this time sync is NOT suitable for systems which require a high degree of time accuracy, such as SCADA systems.

As such it is recommend that Windows Time/w32time is disabled and an alternative suitable solution as detailed below is used.

Solution

An external time synchronisation client should be used, for example NTP for Windows, which can keep server hardware clocks in sync better than Microsoft's implementation of Windows Time.

With some software solutions, such as NTP, multiple servers can be defined as a time source providing reliability in case of a time source failure. The current time for any time sync application should be sourced from a suitable external time source such as a GPS device or an Internet time source, typically SCADA systems should not directly connect to the Internet and so a intermediary time source device should be used, such as a firewall or server within a DMZ environment.

Defining where different time sources can connect to is important to ensure that suitable time synchronisation can occur at all times and system security is easy to manage, for example:

  • All Geo SCADA servers connect to the one or two provided external time sources

 

  • All machines acting as ViewX client connect only to the time synchronisation process running on the Geo SCADA servers for their time, which servers may depend on where these ViewX clients can connect to

 

  • One of the primary Geo SCADA servers is configured to use its local time as a valid time source (where the software allows it) so that should the SCADA system become isolated then time synchronisation can be maintained, even if the time is inaccurate, until such time as the more accurate time sources are available

 

  • Any application servers should either connect to the Geo SCADA servers for their source of time or an alternative time source, depending on how the application server resides within the network

 

  • Servers located within a DMZ should NOT source their data from the primary Geo SCADA servers to minimise surface area of attack


Ensure that any third party time software is kept up to date and suitable ACLs are configured in both network and host based applications to minimise the exposure of any time software to attack. Time synchronization products are a common attack vector for computer systems.

Ensure that any application that is used for time synchronisation has the minimum required permissions, this typically includes:

  • Ability to change a server's time

 

  • Network access permissions

 

  • Run as a service


Whilst an administrator or power user may have the required permissions, best practice is to create a new user and specifically assign the relevant permissions, with additional policies applied to the user to restrict other permissions such as the ability to log in at a console.

Go: Home Back

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore