My customer has a broken PowerTag Link HD in a panel and wants to replace this for a PAS600.
He can not unpair the old PowerTags and pair this with the PAS600
What is the correct workaround?
BR Geeke Pouw
Link copied. Please paste this link to share this article on your social media post.
we found the solution;
More less general procedure for Powertags:
You need first for powertag to lose communication with a gateway (blinking red). You can do this by powering down the gateway for example. Then after 200 (better 300) seconds, powertag starts to blink red fast (once/second), then you need to remove power to the powertag and put it back on, then powertag can be paired to another gateway (blinking fast orange).
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa242973_brid ,
Please describes the symptom for the "broken" PowerTag Link.
Depending on your answer, we may have a solution.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
problem with the power in a demo panel...... they had a small BBQ 😁
now they want to replace i for a PAS600
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa242973_brid ,
In this case, there is no workaround... product must be replaced.
Because you cannot load a configuration file from a PowerTag Link to a Panel Server you will need to restart the commissioning from scratch:
Regards,
Link copied. Please paste this link to share this article on your social media post.
we found the solution;
More less general procedure for Powertags:
You need first for powertag to lose communication with a gateway (blinking red). You can do this by powering down the gateway for example. Then after 200 (better 300) seconds, powertag starts to blink red fast (once/second), then you need to remove power to the powertag and put it back on, then powertag can be paired to another gateway (blinking fast orange).