"Modbus Gateway" option of Com'X200 User Manual 2014/12?

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • "Modbus Gateway" option of Com'X200 User Manual 2014/12?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
QuanGUO
Lieutenant QuanGUO Lieutenant
Lieutenant

Posted: ‎2015-01-07 10:38 PM

0 Likes
1
893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-01-07 10:38 PM

"Modbus Gateway" option of Com'X200 User Manual 2014/12?

Hi Team,

I download the latest user manual of Com'X200 from http://shoppingkiosk.schneider-electric.com/ , which was released in 12/16/2014. I found the Modbus gateway would be an option in the setting profile.

5517

But it seems there is not the option in Web setting page. My Com'X 200 firmware is v1.1.20. What's version of firmware supported the field option? or Is any advanced web page enabled the setting, it looks like http://<EGX300_IP>/device_type_gen_enable.shtml ?

5518


Thanks,

Quan

Tags (3)
  • Tags:
  • 200
  • com'x
  • gateway
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2015-01-15 05:35 AM

0 Likes
0
799
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-01-15 05:35 AM

Hello Quan

The modbus gateway is a feature available in Com'X 200 version 1.1 (thus your version V1.1.20 includes this feature)

There are 2 conditions to use this feature :

  • You must enable it. By default this is not the case,because this Com'X has been designed for publishing data to web sytes, using more secured protocoles
  • In order to reduce the syber attack thread, this gateway feature is not available for some interfaces.

This modbus gateway feature is not available for interface that are only used for publication :

eg : The GPRS modem, the Eth1 interface in the configuration of "2 separate port"

This modbus gateway feature is available for interface that are not only used for publication :

eg : the Eth2 interface  and the Eth1 interface in the configuration of "2 switched port"

This is described in pages 35 and 36 of the design guide (ref SLTED113016EN)

See Answer In Context

Reply
Reply 1
Anonymous user
Not applicable

Posted: ‎2015-01-15 05:35 AM

0 Likes
0
800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-01-15 05:35 AM

Hello Quan

The modbus gateway is a feature available in Com'X 200 version 1.1 (thus your version V1.1.20 includes this feature)

There are 2 conditions to use this feature :

  • You must enable it. By default this is not the case,because this Com'X has been designed for publishing data to web sytes, using more secured protocoles
  • In order to reduce the syber attack thread, this gateway feature is not available for some interfaces.

This modbus gateway feature is not available for interface that are only used for publication :

eg : The GPRS modem, the Eth1 interface in the configuration of "2 separate port"

This modbus gateway feature is available for interface that are not only used for publication :

eg : the Eth2 interface  and the Eth1 interface in the configuration of "2 switched port"

This is described in pages 35 and 36 of the design guide (ref SLTED113016EN)

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore