Hi Team,
I download the latest user manual of Com'X200 from http://shoppingkiosk.schneider-electric.com/ , which was released in 12/16/2014. I found the Modbus gateway would be an option in the setting profile.
But it seems there is not the option in Web setting page. My Com'X 200 firmware is v1.1.20. What's version of firmware supported the field option? or Is any advanced web page enabled the setting, it looks like http://<EGX300_IP>/device_type_gen_enable.shtml ?
Thanks,
Quan
Posted: 2015-01-15 05:35 AM
Link copied. Please paste this link to share this article on your social media post.
Hello Quan
The modbus gateway is a feature available in Com'X 200 version 1.1 (thus your version V1.1.20 includes this feature)
There are 2 conditions to use this feature :
This modbus gateway feature is not available for interface that are only used for publication :
eg : The GPRS modem, the Eth1 interface in the configuration of "2 separate port"
This modbus gateway feature is available for interface that are not only used for publication :
eg : the Eth2 interface and the Eth1 interface in the configuration of "2 switched port"
This is described in pages 35 and 36 of the design guide (ref SLTED113016EN)
Posted: 2015-01-15 05:35 AM
Link copied. Please paste this link to share this article on your social media post.
Hello Quan
The modbus gateway is a feature available in Com'X 200 version 1.1 (thus your version V1.1.20 includes this feature)
There are 2 conditions to use this feature :
This modbus gateway feature is not available for interface that are only used for publication :
eg : The GPRS modem, the Eth1 interface in the configuration of "2 separate port"
This modbus gateway feature is available for interface that are not only used for publication :
eg : the Eth2 interface and the Eth1 interface in the configuration of "2 switched port"
This is described in pages 35 and 36 of the design guide (ref SLTED113016EN)