modbus serial communication to P342020
Good day friends,
Im trying to receive modbus data from a power meter METSEPM5110 to controller P342020 which has serial modbus rj45 port. The meter has D1, D0, C and Shield terminals.
On the controller side (P342020) RJ45 port, I identified 4 and 5 pins are D1 and D0 respectively and pin 8 is Common. I connected accordingly using a terminal block.
Using the READ_VAR, I am not receiving data from meter.
baud rate is set to 9600, parity even
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
In Control Expert, did you setup the M340's serial port as a 2 wire RS485 modbus master running at 9600 baud with even parity? Did you change the default speed of the METSEPM5110 from 19200 to 9600?
If those are both setup then:
- Try swapping D1 and D0.
- Try using the serial port on your computer or a USB to serial converter. (via modscan/kepware/topserver/etc.)
- Post your code here so we can review it.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Solved brother. There was 1 offset in the modbus register. When I gave register number one less than in register in read var, data was read.
Thankyou