iEM2455 & PAS800 as Energy server

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • iEM2455 & PAS800 as Energy server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
106
Guillaume_Evrard
Captain Guillaume_Evrard Captain
51
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
32
View All
Related Products
product field
Schneider Electric
Acti 9 iEM2000

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Horacio1
Lieutenant JG Horacio1 Lieutenant JG
Lieutenant JG

Posted: ‎2023-11-02 03:17 PM

0 Likes
15
2029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-02 03:17 PM

iEM2455 & PAS800 as Energy server

Hello
I would like to know if any of you have been able to use the iEM2455 with the PAS800 using custom model, I have already created a model for it, but everytime I add the device using the model the PAS800´s LED start blinking orange, I hope you guys can help me, Regards.
  • Thumbnail of Acti 9 iEM2000
    Schneider Electric
    Acti 9 iEM2000
View products (1)
Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 15
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-11-05 09:29 PM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-05 09:29 PM

Hello,

Are you able to see measurements ?

Have you checked the modbus com diag for this device?

In the PAS status what is being reported to identify why you have orange status ?

Kind Regards,

 

Reply
Horacio1
Lieutenant JG Horacio1 Lieutenant JG
Lieutenant JG

Posted: ‎2023-11-06 12:54 PM

0 Likes
1
1986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-06 12:54 PM

Thanks Guillaume,

the problem is that for now that meter is not supported by the PAS800, so I have to build a custom model which is working just fine.

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-11-06 09:27 PM

0 Likes
0
1978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-06 09:27 PM

hello,

Your question is how to build a custom model for IEM 2455 ?

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-11-07 04:44 AM

0 Likes
0
1966
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-07 04:44 AM

Hello @Horacio1 , 

If the front LED of the Panel Server is blinking orange, it means that the PAS800 has a communication issue with a device (in your case, the iEM2455). You can check on Maintenance -> System Monitoring to have more information about the reason:

Romain_Polette_0-1699360641178.png

 

Keep in mind to use the Modbus Register Address when you create your custom model with EPC Web. Currently you have a difference in the Modbus implementation between other range of iEM meters and the iEM2435/2455. Please read carefully the iEM2455 Modbus documentation.

Romain_Polette_1-1699360817785.png

 

A good start could be to identify what is the reason of the communication loss:

  • bad wiring ?
  • wrong settings on Panel Server + iEM2455 ?
  • Modbus Exception returned ?

If you cannot identify the root cause, better check with tech support by providing the SysLog of the Panel Server.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
AndersDahlskog
Lieutenant AndersDahlskog Lieutenant
Lieutenant

Posted: ‎2023-11-09 11:48 PM

0 Likes
0
1945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-09 11:48 PM

Hello

In my opinion, iEM2455 is replacing iEM2155 that is a supported device i PAS800, then iEM2455 also should be this to make it easy for customers that is using this 1-phase meters with PAS800 as a local energy server.

 

BR/Anders

Reply
Patricio
Crewman Patricio
Crewman

Posted: ‎2024-10-25 02:27 PM

0 Likes
0
1064
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-25 02:27 PM

Hello

Any one have the template for the register map? i want to load it on an comX 510.

Thanks.

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-11-04 05:18 AM

0 Likes
2
1026
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-04 05:18 AM

Hello @Patricio , 

iEM2455 register list is here:

https://www.productinfo.schneider-electric.com/iem2435_iem2455/iem2435-iem2455-user-manual/iEM2435%2...

 

You need to create your own Com'X custom model with this mapping. You cannot upload a Panel Server template to the Com'X.


Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
JakeTr
Crewman JakeTr Crewman
Crewman

Posted: ‎2025-08-27 06:50 PM

0 Likes
0
119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-27 06:50 PM

Hi, before I create one, does anyone have custom model for iEM2455 for use on PAS800 please?

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-08-27 08:45 PM

1 Like
0
114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-27 08:45 PM

hello @JakeTr,

Find 3 custom models for iEM2455 found in EPC W (26 measurements), I do not know if they are working, measurement names might defer.

Kind Regards

Attachments
models-export-28-08-2025-05-42.zip
Reply
Patricio
Crewman Patricio
Crewman

Posted: ‎2025-08-28 10:14 AM

0 Likes
0
99
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-28 10:14 AM

Hi Romain,

 

I used the template of iem2050 and it gives me the exact register, but when i try to connect to PME 2021 it gives me an error, i used DTE to try to get voltage and frecuency but i cant see it.

 

The error its a common error, Se produjo un problema al procesar su solicitud.

 

Reply
Patricio
Crewman Patricio
Crewman

Posted: ‎2025-08-28 10:16 AM

0 Likes
0
99
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-28 10:16 AM

Hi @Romain_Polette i used the template of iem2050 and it matches perfectly, but when i try to connect it to PME 2021 it gives me an general error.

 

I used DTE to get frecuency and voltage but dont work.

Reply
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2025-08-28 11:50 PM . Last Modified: ‎2025-08-29 12:07 AM

0 Likes
2
96
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-28 11:50 PM

Hi @Patricio @JakeTr 
In case of, iEM2455 is natively supported (so usually no need of custom model) by Panel Server since firmware 001.010.000 so long time ago (current firmware is 002.003.000)

Eric_HAVAS_0-1756450135988.png
Regards
Eric

 

Reply
Patricio
Crewman Patricio
Crewman

Posted: ‎2025-08-29 12:17 AM

0 Likes
0
13
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-29 12:17 AM

Hi @Eric_HAVAS , i have it on comX and Pas600 but i cant configure it on Power Monitoring Expert, it gives me an common error.

 

I have PME 2021, i hope anyone can help me.

 

Thank you!

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-08-29 12:19 AM . Last Modified: ‎2025-08-29 12:24 AM

0 Likes
0
90
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-29 12:19 AM

Hi @Patricio , 

 

I understand the following:

  • some iEM2455 connected as a downstream devices to a Com'X 510
  • Com'X 510 connected as a "Site" + iEM2455 as "devices" under PME Management Console.

Not a good idea to use the iEM2055 model (both for Com'X and PME) to communicate with iEM2455. There is a known discrepency between Modbus table of iEM2055 and iEM2455. And iEM2055 (limited to 9600 bds) has a specific polling method unlike our other iEM range.

 

For Com'X, please create the iEM2455 model from scratch.

For PME2021 please use the official iEM2455 DTE model.

 

In your system, Com'X can be a transparent Modbus TCP gateway for your field devices and it may not necessary to add them (Custom Model) on Com'X interface.

 

If PME is your main monitoring system, better use the official DTE driver and let PME poll the iEM2455 through the Com'X.

 

If you have added some devices under Com'X interface, it is important to declare the devices with there Com'X "Local ID" (and not the slave ID).

Regards,

 

Romain POLETTE
Solution Architect - France Operations
Reply
JakeTr
Crewman JakeTr Crewman
Crewman

Posted: ‎2025-08-29 07:52 PM . Last Modified: ‎2025-08-29 07:52 PM

1 Like
0
57
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-29 07:52 PM

Hi @Eric_HAVAS, thank you kindly for the advice.

My PAS was running old firmware 1.6, when update to latest 2.3 this has resolved the issue.

Thanks!

Kind Regards,

Jake

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore