iEM2455 & PAS800 as Energy server
- Labels:
-
troubleshooting
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello,
Are you able to see measurements ?
Have you checked the modbus com diag for this device?
In the PAS status what is being reported to identify why you have orange status ?
Kind Regards,
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thanks Guillaume,
the problem is that for now that meter is not supported by the PAS800, so I have to build a custom model which is working just fine.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
hello,
Your question is how to build a custom model for IEM 2455 ?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Horacio1 ,
If the front LED of the Panel Server is blinking orange, it means that the PAS800 has a communication issue with a device (in your case, the iEM2455). You can check on Maintenance -> System Monitoring to have more information about the reason:
Keep in mind to use the Modbus Register Address when you create your custom model with EPC Web. Currently you have a difference in the Modbus implementation between other range of iEM meters and the iEM2435/2455. Please read carefully the iEM2455 Modbus documentation.
A good start could be to identify what is the reason of the communication loss:
- bad wiring ?
- wrong settings on Panel Server + iEM2455 ?
- Modbus Exception returned ?
If you cannot identify the root cause, better check with tech support by providing the SysLog of the Panel Server.
Regards,
Solution Architect - France Operations
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello
In my opinion, iEM2455 is replacing iEM2155 that is a supported device i PAS800, then iEM2455 also should be this to make it easy for customers that is using this 1-phase meters with PAS800 as a local energy server.
BR/Anders
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello
Any one have the template for the register map? i want to load it on an comX 510.
Thanks.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Patricio ,
iEM2455 register list is here:
You need to create your own Com'X custom model with this mapping. You cannot upload a Panel Server template to the Com'X.
Regards,
Solution Architect - France Operations