ecostruxure Power monitoring expert installation and costs

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • ecostruxure Power monitoring expert installation and costs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Power Monitoring Expert
product field
Schneider Electric
PowerLogic PM5000 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
GIAS2022
GIAS2022
Cadet

Posted: ‎2023-05-28 09:33 AM

0 Likes
2
2956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-28 09:33 AM

ecostruxure Power monitoring expert installation and costs

Hello everyone,

I have to monitor the energy for our building. I am using for the first time
Schneiner electric components, I don't know a lot about it and  need support.
The project consists of 19 PoweLogic PM5000 series devices that are to communicate with an EBX210/510 via Modbus. The energy data must then be transmitted to a computer via Ethernet and displayed there.
My questions are :
Is Ecostruxure Power Monitoring Expert software free for one node (one machine)? If not where can I find the cost of my solution?
Is EBX/Com'X 210 suitable or should I use something else here?
i will be also thankfull for any other suitable Propose.

thank you very much
  • Thumbnail of EcoStruxure™ Power Monitoring Expert
    Schneider Electric
    EcoStruxure™ Power Monitoring Expert
  • Thumbnail of PowerLogic PM5000 series
    Schneider Electric
    PowerLogic PM5000 series
View products (2)
Labels
  • Labels:
  • Legacy Gateways & Energy Servers
Tags (3)
  • Tags:
  • english
  • Frensh
  • german
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2023-06-09 08:58 AM

1 Like
0
2852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-09 08:58 AM

Hello @GIAS2022 

 

Com'X210/510 is the previous generation of gateway and is now replaced by Panel server (but the both product are suypported in this forum). At the end of my post, I add a link to a pined post of this  forum to discover Panel Server and all the main docs/assets for the gateway


In a nutshell, 3 types of architectures are possible with panel server:

 

  • Archi1: Panel server connected to a on premise Modbus TCP client (such as PME mentionned previously by Charles). in this case , the Panel Server act as a transparent gateway and just forward modbus traffic between the upper Modbus TCP client and the downstream products. A software such as PME is powerfull to leverage the better of all the connected meters and monitor your electrical network.
  • Archi2: Panel Server connected to a SE CLoud Advisor (such Energy Hub for example) to achieve your business and sustainability goals with energy management (EEH link)
    https://www.se.com/ww/en/product-range/88215214-ecostruxure-energy-hub/?preferredCountry=yes
  • Archi3: Panel Server used as a local Energy Server without upper sofware cloud application to log locally the consumption meters and follow consumption trends in web page /export in csv, be notified of alarms by email). This archi is less powerfull than the 2 previous one but more cost competitive because no software/ subsription are needed in this case.

Hope it will help you to start. Contact your local SE office if your need help and more details about our offers.

Best regards

 

https://community.se.com/t5/Gateways-and-Energy-Servers/EcoStruxure-Panel-Server-Our-new-Generation-...

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions

See Answer In Context

Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-05-30 09:17 AM . Last Modified: ‎2025-11-24 04:15 AM

1 Like
0
2915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-30 09:17 AM

Hello @GIAS2022 ,

 

PME is not free, there are license costs. As for pricing I would recommend contacting your local Schneider sales team for a quote. 

 

Having 19 modbus devices in a single serial loop is likely not going to perform as well as you would want. Daisy Chain Calculator from https://ecoxpert.se.com/power-management-systems/power-management-software/power-monitoring-expert/d... -> tools or Daisy Chain Calculator can help determine if you need more gateway devices. A lot will depend on the type of PM5000 meter, PM53XX very different than PM556X, and what you will want to do in PME. This is not because of the gateway choose, serial communications are slow and always the bottleneck. 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2023-06-09 08:58 AM

1 Like
0
2853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-09 08:58 AM

Hello @GIAS2022 

 

Com'X210/510 is the previous generation of gateway and is now replaced by Panel server (but the both product are suypported in this forum). At the end of my post, I add a link to a pined post of this  forum to discover Panel Server and all the main docs/assets for the gateway


In a nutshell, 3 types of architectures are possible with panel server:

 

  • Archi1: Panel server connected to a on premise Modbus TCP client (such as PME mentionned previously by Charles). in this case , the Panel Server act as a transparent gateway and just forward modbus traffic between the upper Modbus TCP client and the downstream products. A software such as PME is powerfull to leverage the better of all the connected meters and monitor your electrical network.
  • Archi2: Panel Server connected to a SE CLoud Advisor (such Energy Hub for example) to achieve your business and sustainability goals with energy management (EEH link)
    https://www.se.com/ww/en/product-range/88215214-ecostruxure-energy-hub/?preferredCountry=yes
  • Archi3: Panel Server used as a local Energy Server without upper sofware cloud application to log locally the consumption meters and follow consumption trends in web page /export in csv, be notified of alarms by email). This archi is less powerfull than the 2 previous one but more cost competitive because no software/ subsription are needed in this case.

Hope it will help you to start. Contact your local SE office if your need help and more details about our offers.

Best regards

 

https://community.se.com/t5/Gateways-and-Energy-Servers/EcoStruxure-Panel-Server-Our-new-Generation-...

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore