Possible to disable PowerTag alarms in Panel Server?
Gateways and Energy Servers
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Possible to disable PowerTag alarms in Panel Server?
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
59
Randi_Dolan
46
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander
Posted: ‎2023-05-28 07:46 AM . Last Modified: ‎2023-05-28 07:47 AM
1733
Hi All,
In the legacy gateway PowerTag Link, we can disable some PowerTag alarms on the webpage. Will this function be implemented in Panel Server in the future? Or are there any other ways to disable the PowerTag alarm? Thanks
  • Commissioning
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander
Posted: ‎2023-05-29 12:28 AM . Last Modified: ‎2023-05-29 12:30 AM
Yes , it is also implemented in Panel Server.
1)Navigate to Settings > Data Management then select the PowerTag
2) Go to alarms to select or unselect  alarms for this PowerTag (screenshot hereunder)
"zero current" is one of these alarms.
Best regards
Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Replies 4
Thierry_Baudard
Commander
Best regards
Thierry BAUDARD
Stuart_Cheng
Lt. Commander
Posted: ‎2023-05-29 01:07 AM
Hi @Thierry_Baudard ,
Many thanks for your information. May I know start from which firmware version this function was implemented?
Romain_Polette
Kirk
Posted: ‎2023-06-06 01:49 AM
Hello @Thierry_Baudard ,
On PowerTag Link, deactivate an alarm also disable the alarm through Modbus.
Can you confirm if this feature is implemented on Panel Server or not ?
Thanks.
Romain POLETTE
Solution Architect - France Operations
Thierry_Baudard
Commander
Posted: ‎2023-06-09 07:56 AM . Last Modified: ‎2023-06-09 09:05 AM
Hi @Romain_Polette
After analysis, it only disables alarms in web page and for cloud publication ...but does not disable alarms via modbus registers.
BR
Thierry BAUDARD