Hi All,
In the legacy gateway PowerTag Link, we can disable some PowerTag alarms on the webpage. Will this function be implemented in Panel Server in the future? Or are there any other ways to disable the PowerTag alarm? Thanks
Link copied. Please paste this link to share this article on your social media post.
Hello,
Yes , it is also implemented in Panel Server.
1)Navigate to Settings > Data Management then select the PowerTag
2) Go to alarms to select or unselect alarms for this PowerTag (screenshot hereunder)
"zero current" is one of these alarms.
Best regards
Link copied. Please paste this link to share this article on your social media post.
Hello,
Yes , it is also implemented in Panel Server.
1)Navigate to Settings > Data Management then select the PowerTag
2) Go to alarms to select or unselect alarms for this PowerTag (screenshot hereunder)
"zero current" is one of these alarms.
Best regards
Link copied. Please paste this link to share this article on your social media post.
Hi @Thierry_Baudard ,
Many thanks for your information. May I know start from which firmware version this function was implemented?
Link copied. Please paste this link to share this article on your social media post.
Hello @Thierry_Baudard ,
On PowerTag Link, deactivate an alarm also disable the alarm through Modbus.
Can you confirm if this feature is implemented on Panel Server or not ?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
After analysis, it only disables alarms in web page and for cloud publication ...but does not disable alarms via modbus registers.