Panel server PAS600 Maximum Modbus devices possible

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Panel server PAS600 Maximum Modbus devices possible
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
lalitlambole03
lalitlambole03 Cadet
Cadet

Posted: ‎2025-09-23 12:03 PM

0 Likes
4
506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-23 12:03 PM

Panel server PAS600 Maximum Modbus devices possible

Hello Folks, 

I am using PASS600 as Modbus RTU to TCP/IP converter and trying to connect 16 serial devices at 9600 bps and 500ms polling period on Modbus RTU protocol but there seems to be some issue with this connection. Can anyone please provide clarity on exact number of devices which can be connected in single loop with this setting for PAS600 panel server.

Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-09-23 10:08 PM . Last Modified: ‎2025-09-23 10:14 PM

0 Likes
1
493
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-23 10:08 PM

hello @lalitlambole03 

You have to make your own computations taking into account polling cycle, baudrate, nb of devices polled, answer time, time to revert the RS485 communication and 10ms delay by PAS . Pay attention to the timeout on the PAS (Time it will wait before returning no answer from device if devices are slow). 

Or add one by one and check performance. remember the limit from release note in terms of devices

 

Do not configure the devices in the PAS, use the transparent gateway feature.

Kind Regards

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-09-24 12:19 AM

1 Like
1
484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-24 12:19 AM

Hello @lalitlambole03 , 

16 serial devices connected to Panel Server and poll frequency @ 9600 Bds seems "comfortable". 

 

Communication issues on serial bus can have many different root causes:

  1. bad quality wiring of the bus (shield continuity, ground reference, polarization, termination resistor)
  2. Modbus stack of your serial devices (low Modbus performances, response time)
  3. Modbus frames sent by your Modbus Master (too many consecutive registers not managed by serial devices, bad addressing)
  4. Serial line parameters (settings not aligned between gateway and serial devices, gateway and Modbus Master timeout) 

To better understand your issue:

  • Do you have any Modbus exception displayed on your Master ?
  • Can you poll the serial devices directly from the PAS600 interface ? Settings > Modbus devices > Modbus registers read
  • Is this working with only 1 or less than 10 devices ?
  • Did you activate Modbus TCP services on PAS600 ?

Regards, 

 

 

Romain POLETTE
Solution Architect - France Operations
Reply
lalitlambole03
lalitlambole03 Cadet
Cadet

Posted: ‎2025-10-02 11:39 AM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-02 11:39 AM

Thank you I will try adding them one by one using transparent gateway

 

Reply
lalitlambole03
lalitlambole03 Cadet
Cadet

Posted: ‎2025-10-02 11:43 AM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-02 11:43 AM

Yes TCP/IP is enabled, and individual devices can be polled also the loop is working fine for less than 10 devices in loop. 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore