PAS600 Connected to two VLANS

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • PAS600 Connected to two VLANS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Maja555
Lieutenant | EcoXpert Master Maja555 Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-08-15 09:41 PM

0 Likes
12
3049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-15 09:41 PM

PAS600 Connected to two VLANS

Hello,

 

I understand the switched mode configuration at the moment seems to be only for separating downstream devices. 

 

We have customers requesting the functionality that two different VLANS/supervisory systems can read the device. 

 

Will this be implemented?

 

Thanks,

Labels
  • Labels:
  • Commissioning
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-08-22 10:00 PM . Last Modified: ‎2023-08-22 10:02 PM

0 Likes
0
2939
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-22 10:00 PM

Hello @Maja555,

All settings are available on the web pages.

Guillaume_Evrard_0-1692766868622.png

What I was saying is that Eth2 even if it shown as identical to ETH1 can not be used for cloud publication.

Comx did not have the capability to have a gateway IP address for port 2 It was only the local LAN.

See Answer In Context

Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2023-08-28 12:07 AM

1 Like
0
2890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-28 12:07 AM

Hello @Maja555 ,

 

Even if web page propose to fill a IP gateway for ETh2. value filled is not used in background by the firmware (This parameter should be removed of the web page in  a future Panel Server firmware version).

Obvously, as of today, ETH 2 is only for a local ethernet network for connection of downstream Modbus TCP products without possibility to communicate outside this private network.

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions

See Answer In Context

Reply
Replies 12
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-08-17 12:20 AM

0 Likes
1
3030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-17 12:20 AM

Hello,

Switched mode is not seggregating anything. Depends on what you call VLAN. If you refer to VLAN using VLAN Id you willl need a L3 switch or a router to map to different LANs.

If you want to access the devices using 2 LANs, suggest to use separated port, enable modbus tcp server services on ETH1 and ETH2. ETH1 and ETH2 should have different network settings.

 

 

Reply
Maja555
Lieutenant | EcoXpert Master Maja555 Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-08-20 09:19 PM . Last Modified: ‎2023-08-20 09:21 PM

0 Likes
0
2983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-20 09:19 PM

Hi Guillaume,

 

I was talking about separated ports, apologies got the terminology wrong.

 

As you can see for separated ports there is no where to enter individual gateway IPs for each port:

 

Maja555_1-1692591496404.png

 

There is only one gateway IP setting that can be entered here presumably for ETH1:

Maja555_3-1692591588743.png

 

 

We need to be able to enter two gateway IPs?

 

Thanks,

 

Reply
Szymon_Hochół
Captain Szymon_Hochół Captain
Captain

Posted: ‎2023-08-21 01:41 AM

0 Likes
3
2976
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-21 01:41 AM

Hi @Maja555

this could be a limitation of EPC software. When you open gateway's webpage and go to network settings, you will be able to set up different Default Gateway for each port.

 

BR

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-08-21 11:55 PM

0 Likes
2
2959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-21 11:55 PM

I confirm all settings are available from the web pages.

Even if it seems that 2 ports are identicals, they have different usage. Cloud connectivity is only available on Port 1.

Reply
Maja555
Lieutenant | EcoXpert Master Maja555 Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-08-22 04:28 PM

0 Likes
1
2942
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-22 04:28 PM

Hi @Guillaume_Evrard 

 

So does that mean the Gateway IP setting is not available for Port 2? 

 

Will this ever change as this was a funciton the ComX had?

 

Thanks,

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-08-22 10:00 PM . Last Modified: ‎2023-08-22 10:02 PM

0 Likes
0
2940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-22 10:00 PM

Hello @Maja555,

All settings are available on the web pages.

Guillaume_Evrard_0-1692766868622.png

What I was saying is that Eth2 even if it shown as identical to ETH1 can not be used for cloud publication.

Comx did not have the capability to have a gateway IP address for port 2 It was only the local LAN.

Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2023-08-28 12:07 AM

1 Like
0
2891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-28 12:07 AM

Hello @Maja555 ,

 

Even if web page propose to fill a IP gateway for ETh2. value filled is not used in background by the firmware (This parameter should be removed of the web page in  a future Panel Server firmware version).

Obvously, as of today, ETH 2 is only for a local ethernet network for connection of downstream Modbus TCP products without possibility to communicate outside this private network.

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Reply
Maja555
Lieutenant | EcoXpert Master Maja555 Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-09-04 07:35 PM

0 Likes
0
2848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-09-04 07:35 PM

Hi @Thierry_Baudard thanks very much for the response and clarification. This makes more sense now.  Would be great to have this clearly explained in the usermanual without a lot of refernces to cloud connectivity. Cheers. 

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-09-05 02:34 AM

1 Like
2
2836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-09-05 02:34 AM

Hi @Maja555 , 

 

This does no make sense to have a "Gateway IP" parameter on ETH2 if you are in ETH Separated Mode.

The "Gateway" must be seen as an intermediate device (like a router) to enable your LAN to communicate with another LAN or the Internet. Devices connected to ETH2 on Separated Mode are not allowed to communicate directly with upstream system.

 

On Com'X510 the Gateway IP parameter was global (as mentioned by Guillaume). This was less confusing than the current PAS interface.

Romain_Polette_2-1693905319768.png

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-09-06 12:30 AM

0 Likes
1
2808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-09-06 12:30 AM

@Romain_Polette, I disagree that it does not make sense, I would say Gateway for ETH2 shall be removed from the interface....

Reply
Szymon_Hochół
Captain Szymon_Hochół Captain
Captain

Posted: ‎2023-09-07 12:01 AM

1 Like
0
2798
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-09-07 12:01 AM

Hi @Guillaume_Evrard, it will be removed in future firmware releases.

Reply
Stellan
Stellan
Cadet

Posted: ‎2025-10-02 12:06 PM

0 Likes
0
651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-02 12:06 PM

Hi!
Is there a solution to connect to two separate VLANs? I have a customer who wants to read energy measurements via Modbus to one IP address, and at the same time read alarm functions via Modbus to another IP address from the same Modbus device (circuit breaker).

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore