Hi there community,
Setting up two water flow meters (1L per pulse) into the two digital inputs atop a PAS600L (Fw Vers 002.003.000, Hw Vers 002.000.000).
Attached are screenshots for the DI's configuration, sampling settings, and monitoring data (inc advanced).
water is not turned on to site yet, however I believe I should simply be able to bridge the DI input terminals to simulate a pulse, however for the life of me I cannot see any data coming back in conducting this test.
Is there some setting I'm missing or am I testing inefficiently?
Any help appreciated.
Posted: 2025-10-01 09:28 PM . Last Modified: 2025-10-01 09:29 PM
Link copied. Please paste this link to share this article on your social media post.
Hi there,
By bridging the input directly you are acting as a dry contact. The PAS600L requires external excitation for this in the form of a 24V DC power supply. See page 10/20 of the install manual attached.
Posted: 2025-10-01 09:28 PM . Last Modified: 2025-10-01 09:29 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Thankyou!
Link copied. Please paste this link to share this article on your social media post.
Please see link to water meters installed onsite.
I note they are rated 6v switching . Possibly a stupid question, does that mean we cannot send 24v to the pulse meter or am I misunderstanding the 6v rating?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @BrettWabbis ,
It seems your reed switch is not compatible with 24 VDC (6 VDC). So you cannot connect your pulse meter directly on the PAS600L power supply.
Check if :
Many other water meters are using a 24 AC/DC compatible reed switch.
Regards,