PAS600 + M251 data mapping table
Gateways and Energy Servers
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • PAS600 + M251 data mapping table
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
59
Randi_Dolan
46
Alexander_Akulov
Crewman Alexander_Akulov Crewman
Crewman
Posted: ‎2024-06-06 02:51 AM . Last Modified: ‎2024-06-06 03:04 AM
1397
Hello Team! We had a difficulties in reading data from PLC Modicon M251 to upper ECS PLC via modbus TCP/IP.
According to the project the ECS PLC should be connected to the M251 (as single data concentrator for the sensors) not the PAS600. So all the signals from all PAS600 will be re-mapped in new addresses in the M251.
The configuration is made in LV SMD.
We need to know which modbus registers we will read from M251.
  • Commissioning
  • troubleshooting
Romain_Polette
Kirk
Posted: ‎2024-06-06 05:12 AM
Hello @Alexander_Akulov ,
If you need to know M251 registers related to LV SMD application, please check this thread:
https://community.se.com/t5/Gateways-and-Energy-Servers/Looking-For-SMD-LV-Modbus-User-Table/td-p/47...
Romain POLETTE
Solution Architect - France Operations
Replies 4
Romain_Polette
Kirk
Romain POLETTE
Guillaume_Evrard
Captain
Posted: ‎2024-06-06 09:19 PM
1358
hello @Alexander_Akulov ,
Not sure that PLC supports RSTP, for me ETH1 is a basic switch.
@Romain_Polette  has provided the right link, all "functions" are grouped by range of address in the PLC.
Idea to have the PLC is to get the alarming made by the PLC ( compute the various thresholds).
If you just need the temperature readings SMD is not mandatory.
Kind Regards
Alexander_Akulov
Crewman
Posted: ‎2024-06-07 03:20 AM
1344
Hello @Guillaume_Evrard
We have temperature measurements only. We need to send values in upper level to ECS. Which registers should we read from PLC itself in that case?
Thank you in advance!
Guillaume_Evrard
Captain
Posted: ‎2024-06-07 04:07 AM
hello,
As mentioned by Romain : https://community.se.com/t5/Gateways-and-Energy-Servers/Looking-For-SMD-LV-Modbus-User-Table/td-p/47...