Looking For SMD LV Modbus User Table
Gateways and Energy Servers
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Looking For SMD LV Modbus User Table
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
59
Randi_Dolan
46
Sachin_8085
Crewman Sachin_8085 Crewman
Crewman
Posted: ‎2024-05-12 09:32 PM
1881
In one of project Power Tag link is use to communicate with TH110 and CL110 sensors and Output of Power Tag link is given to SMD. SMD is configure using SMD LV Tool and and one output is going to the HMI and from another output is going to customer Scada. So I required  SMD LV Modbus user table , so that I can give Modbus address to customer.
  • Commissioning
  • troubleshooting
Guillaume_Evrard
Captain
Posted: ‎2024-05-28 08:55 PM
1
1820
hello here it is, I am not sure this is the last version but should work.
Pay attention on the wiring of ETH1 and ETH2 and on the configuration of the IP adresses as you have to configure 2 different networks. Easiest option is to have Magellis and scada on port 1.
Replies 4
Romain_Polette
Kirk
Posted: ‎2024-05-28 04:43 AM
1831
Hello @Sachin_8085 ,
Regarding the Modbus table for SMD LV Switchboard, I will let @UdhayakumarAK answer. Not sure this can be shared with customers.
If not possible to share, solution will be poll directly each Powertag Link to read CL110 and TH110 values.
CL110 and TH110 Modbus Registers are not available on the Powertag Link documentation, but in the Panel Server doc.
If you need alarms from the SMD LV, then Modbus table is required because managed at M251 PLC level.
FYI: SMD for LV Switchboard is native to our Software Power Monitoring Expert and Power Operation.
Romain POLETTE
Solution Architect - France Operations
Guillaume_Evrard
Captain
1
1821
Sachin_8085
Crewman
Posted: ‎2024-05-28 09:26 PM
Thank You.
Sachin_8085
Crewman
Thank you.