In one of project Power Tag link is use to communicate with TH110 and CL110 sensors and Output of Power Tag link is given to SMD. SMD is configure using SMD LV Tool and and one output is going to the HMI and from another output is going to customer Scada. So I required SMD LV Modbus user table , so that I can give Modbus address to customer.
Link copied. Please paste this link to share this article on your social media post.
hello here it is, I am not sure this is the last version but should work.
Pay attention on the wiring of ETH1 and ETH2 and on the configuration of the IP adresses as you have to configure 2 different networks. Easiest option is to have Magellis and scada on port 1.
Link copied. Please paste this link to share this article on your social media post.
Hello @Sachin_8085 ,
Regarding the Modbus table for SMD LV Switchboard, I will let @UdhayakumarAK answer. Not sure this can be shared with customers.
If not possible to share, solution will be poll directly each Powertag Link to read CL110 and TH110 values.
CL110 and TH110 Modbus Registers are not available on the Powertag Link documentation, but in the Panel Server doc.
If you need alarms from the SMD LV, then Modbus table is required because managed at M251 PLC level.
FYI: SMD for LV Switchboard is native to our Software Power Monitoring Expert and Power Operation.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Thank You.
Link copied. Please paste this link to share this article on your social media post.
Thank you.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.