IFE default username & password has been changed

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • IFE default username & password has been changed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
sesa149897_brid
Lieutenant JG sesa149897_brid Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-21 01:15 PM

0 Likes
12
10194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-21 01:15 PM

IFE default username & password has been changed

Hi Everyone,

This is the brand new IFE module, but the default Username "Administrator" & Password "Gateway" did not work. Error message "Login failed, invalid Username or Password. Please check and try again."

Is there any way to reset the username and password of IFE module back to default one? Thanks

 

Regards,

Khanh

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2021-10-21 01:24 PM

2 Likes
1
10191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-21 01:24 PM

Hello @sesa149897_brid , 

There are some CyberSec changes with latest release of IFE.

https://www.productinfo.schneider-electric.com/ife-eifereleasenote/ife-eife-release-note/English/Rel...


If your IFE has FW 004.004.001 the default credentials are the following:

Login = SecurityAdmin
Pass = AAAAAAAA 

 

This is mentioned in the IFE User Manual:

https://www.productinfo.schneider-electric.com/ifeinterface_userguide_iec/ife-interface-user-guide-i...


Regards, 

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 12
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2021-10-21 01:24 PM

2 Likes
1
10192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-21 01:24 PM

Hello @sesa149897_brid , 

There are some CyberSec changes with latest release of IFE.

https://www.productinfo.schneider-electric.com/ife-eifereleasenote/ife-eife-release-note/English/Rel...


If your IFE has FW 004.004.001 the default credentials are the following:

Login = SecurityAdmin
Pass = AAAAAAAA 

 

This is mentioned in the IFE User Manual:

https://www.productinfo.schneider-electric.com/ifeinterface_userguide_iec/ife-interface-user-guide-i...


Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
sesa149897_brid
Lieutenant JG sesa149897_brid Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-21 01:30 PM

1 Like
0
10187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-21 01:30 PM

it works, thanks a lot!

Tags (1)
  • Tags:
  • english
Reply
vedharaj1994
Crewman vedharaj1994
Crewman

Posted: ‎2025-07-29 04:41 AM

0 Likes
0
1847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-29 04:41 AM

Enerlin X IFE Forget password ? how to open

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-07-29 08:09 AM

1 Like
2
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-29 08:09 AM

Hello @vedharaj1994 , 

For reference LV434002, it is not possible to recover or reset the lost Security Administrator password. The only solution is to replace the IFE LV434002 with a new unit.

 

https://www.se.com/us/en/faqs/FA355521/

 

If you have lost all passwords associated with the Security Administrator roles, it is recommended to contact your local Schneider Electric Customer Care Center for assistance.

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
vedharaj1994
Crewman vedharaj1994
Crewman

Posted: ‎2025-07-31 12:59 AM

0 Likes
0
1812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-31 12:59 AM

 ok thank you. Then one more question answer? com'x510 password i can reset. The default for password  admin. I tried this default possible, but not working.

Reply
vedharaj1994
Crewman vedharaj1994
Crewman

Posted: ‎2025-07-31 01:02 AM

0 Likes
0
1812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-31 01:02 AM

Thank you

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-07-31 02:44 AM

0 Likes
1
1808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-31 02:44 AM

Hello @vedharaj1994 , 

Try this procedure:

https://www.productinfo.schneider-electric.com/comx/5a14ea5846e0fb00018c268b/Com'X%20510%20user%20ma...

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • I tried this password. Not working
Reply
vedharaj1994
Crewman vedharaj1994
Crewman

Posted: ‎2025-07-31 03:12 AM

0 Likes
0
1779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-31 03:12 AM

1000122863.jpg

 

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-07-31 11:05 PM . Last Modified: ‎2025-07-31 11:05 PM

0 Likes
1
1778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-31 11:05 PM

Hello @vedharaj1994 , 

Your IFE has a recent FW. So you need to use "SecurityAdmin" as user name as I mentioned in the begining of this thread.

https://www.productinfo.schneider-electric.com/ifeinterface_userguide_iec/ife-interface-user-guide-i...

 

Regards, 

 

 

Romain POLETTE
Solution Architect - France Operations
Reply
vedharaj1994
Crewman vedharaj1994
Crewman

Posted: ‎2025-08-03 09:42 PM

0 Likes
0
1722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-03 09:42 PM

Yes, now it's work. Thank you

Reply
vedharaj1994
Crewman vedharaj1994
Crewman

Posted: ‎2025-08-03 10:45 PM

0 Likes
0
1722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-03 10:45 PM

Com'X510 i can reset password?  admin admin default password not working

 
 

1000124154.jpg

 

Reply
vedharaj1994
Crewman vedharaj1994
Crewman

Posted: ‎2025-08-03 10:49 PM

0 Likes
0
1722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-03 10:49 PM

Then one more also Com'X510 

1000124157.jpg

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore