Hi Everyone,
This is the brand new IFE module, but the default Username "Administrator" & Password "Gateway" did not work. Error message "Login failed, invalid Username or Password. Please check and try again."
Is there any way to reset the username and password of IFE module back to default one? Thanks
Regards,
Khanh
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa149897_brid ,
There are some CyberSec changes with latest release of IFE.
If your IFE has FW 004.004.001 the default credentials are the following:
Login = SecurityAdmin
Pass = AAAAAAAA
This is mentioned in the IFE User Manual:
Regards,