COM'x Device logged data in PME

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • COM'x Device logged data in PME
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
96
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
41
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
Andy_Hubert
Lieutenant Andy_Hubert Lieutenant
Lieutenant

Posted: ‎2021-09-21 01:30 AM

0 Likes
6
1304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 01:30 AM

COM'x Device logged data in PME

Good Morning,

 

I have a site that is using several com’x 210s to count pulses from wages devices around the site, and we have noticed anomalies in the data.

 

The device is set up in PME to log every 15 minutes, but we keep getting gaps in the logged data, sometimes this gap is a couple of hours, other times it is nearly a whole day.

 

The opposite is also true, the logging may work for 3 hours, or a couple of days, but again this is completely random.

 

There is no sign of any comms issues, and as far as we can see there is nothing wrong with the device type.

 

We have also set a couple of the COM’x to send their on board logged data out as a csv file, and these appear to be full, with no gaps anywhere in the day.

 

Any idea what could be causing this, or any suggestions on how to fix it would be appreciated.

 

Thanks

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2021-10-20 04:22 AM . Last Modified: ‎2021-10-20 04:23 AM

0 Likes
0
1265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-20 04:22 AM

Hi @Andy_Hubert  ,

I confirm also these tests on my own system.

 

Logical Devices created from a Customized Com'X driver are working without any gaps compared to Logical Devices created from native Com'X Driver.

 

Example below. My Com'X and associated pulse meters are the sames, I only used 2 different driver versions.

 

Annotation 2021-10-20 132042.png

 

@Anirban is this possible to consider an update of the Com'X Wage driver on PME ? The current settings for UpdateRates = 300 and Staleness Threshold = 120 are leading to have some gaps in the data.

 

@Andy_Hubert do not forget to put this thread as solved.

 

Thanks.

 

Romain

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 6
Mark_Raftery
Ensign Mark_Raftery Ensign
Ensign

Posted: ‎2021-09-21 01:37 AM

0 Likes
0
1302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 01:37 AM

Good morning Andy,

Just a thought, its not the marked space ratio? ie the flow speeds up and the Com'X is not able to catch the pulse?

Just a though 🙂

KRF Mark

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2021-09-21 02:08 AM . Last Modified: ‎2021-09-21 02:10 AM

0 Likes
4
1300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 02:08 AM

Hi @Andy_Hubert , 

What is your PME version ?

Are you using the default Com'X_WAGES driver for PME ? Or did you customize this driver ?

Did you create Logical Devices for your Pulse Meters ?

 

Com'X data logging + .csv publication and PME data logging are 2 different (and independent) processes. PME driver will only read some Modbus registers of the Com'X and log the values into its ION_Data database.

 

If the DI of the Com'X can detect your Pulse Meters and publish .csv, the issue seems more between Com'X and PME (communication ? ION Services ?).


Check with the Diagnostic Viewer if you can see some issues with the Log Inserter or other services.

Check also for some Warnings or Errors on the System Log (Management Console).

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Andy_Hubert
Lieutenant Andy_Hubert Lieutenant
Lieutenant

Posted: ‎2021-10-12 12:38 AM

0 Likes
3
1287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-12 12:38 AM

Hi,

 

just to answer our questions 

 

What is your PME version ? PME 2020

Are you using the default Com'X_WAGES driver for PME ? Or did you customize this driver ? we have tried both the default driver and custom versions, and both behave the same. 

Did you create Logical Devices for your Pulse Meters ? Yes.

 

We have also checked the logs, and there are no events relating to either the loginserter or device comms.

 

Thanks

 

Andy

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2021-10-12 02:53 AM

1 Like
2
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-12 02:53 AM

Hello @Andy_Hubert ,


I had a remote session with Michail this morning concerning your issue.

 

I updated some parameters in its ComX Custom Drivers according to https://www.se.com/my/en/faqs/FA210245/

 

I propose to let the system run for 48 hours and have an update of the situation just after.

 

Regards, 

Romain

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Andy_Hubert
Lieutenant Andy_Hubert Lieutenant
Lieutenant

Posted: ‎2021-10-20 03:35 AM

0 Likes
1
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-20 03:35 AM

Hi,

 

I made this change to one of the device types on my site, and in 8 days since I did this there have been no gaps in the data.

 

Thanks for the resolution.

 

Andy

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2021-10-20 04:22 AM . Last Modified: ‎2021-10-20 04:23 AM

0 Likes
0
1266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-20 04:22 AM

Hi @Andy_Hubert  ,

I confirm also these tests on my own system.

 

Logical Devices created from a Customized Com'X driver are working without any gaps compared to Logical Devices created from native Com'X Driver.

 

Example below. My Com'X and associated pulse meters are the sames, I only used 2 different driver versions.

 

Annotation 2021-10-20 132042.png

 

@Anirban is this possible to consider an update of the Com'X Wage driver on PME ? The current settings for UpdateRates = 300 and Staleness Threshold = 120 are leading to have some gaps in the data.

 

@Andy_Hubert do not forget to put this thread as solved.

 

Thanks.

 

Romain

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of