How to connect a thermal meter via Modbus RTU?
Gateways and Energy Servers
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • How to connect a thermal meter via Modbus RTU?
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
58
Randi_Dolan
46
maxencevanhove
maxencevanhove Schneider Alumni (Retired)
Posted: ‎2014-08-07 09:33 AM
2026
Dear all,
We are currently facing difficulties trying to get data from an Ultramess 602 thermal meter (see attached doc) into an EGX300 via modbus RTU.
Has anyone of you had experience (preferably successful ones) with connecting Kamstrup/Ultramess meters to EGX's?
If so, how the EGX should be configured?
Many thanks in anticipation!
-Maxence
Tags (3)
  • modbus
  • rtu
  • thermal
QuanGUO
Lieutenant QuanGUO Lieutenant
Lieutenant
Posted: ‎2014-08-18 06:26 PM
Hi Maxence,
Yes, Laurent already pointed out the two key tricks on this:)) Also I would suggest you can try "Modscan" (or another Modbus test tool) to access your device.
4357
4358
4359
Quan
LaurentCoene
Captain LaurentCoene Captain
Captain
Posted: ‎2014-08-18 02:50 AM
1
1875
Hi Maxou!
New 3rd party devices can always be tricky but eventually, you can always get it.
What you need to do is:
-- Play by doing -1 or +1 to the address in the document. That's because sometimes addresses start at 0 and sometimes at 1. So you must try both.
-- Make sure to test inverting the registers. Despite documentation, often, there's some differences
So to test it, choose an easy register to start (an int16), try the -1 and +1 to make this one work. Then you can go to the floats.
It's always painful, but these two tricks always do it for me!
Hope this helps!
QuanGUO
Lieutenant
Hi Maxence,
4357
4358
4359
Quan