Hi
Customer would like to know if EGX300 capable of handling 32pcs PM3255 polling KWh and DI status with 1 minute interval.
Any way to evaluate a suitable design?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi,
The EGX300 FW supports (5, 10, 15, 20, 30, 60) minutes logging intervals. Therefore, there is no 1-minute logging interval supported.
For the 5 minutes logging interval, the EGX300 is capable of handling 32 PM3255 devices polling one topic (KWh). I hope that is helpful. Let me know if you have any questions.
Best Regards,
Link copied. Please paste this link to share this article on your social media post.
Hi Machael, is there any issues with 1 minute logging . I can see the 1 minutes is commented in selection. If restore and reload firmware then tested some logging with 1 minute interval.
Link copied. Please paste this link to share this article on your social media post.
Hi Shrikant,
The 1 minute logging interval is not supported and not tested for the EGX300 (That is why it's commented) and using it might cause communication issues.
Best Regards,