EGX 150 Pin occupancy RJ 45 to RS-485

Gateways and Energy Servers

Get expert answers to your questions regarding Schneider Electric Gateways & Energy Servers, from product selection to implementation and troubleshooting. Collaborate with a global community of experts and peers, get support and share your experiences by subscribing to the Schneider Electric Community Gateways and Energy Servers forum today.

Solved
Sven_Ortmann
Commander Commander
Commander
0 Likes
2
159

EGX 150 Pin occupancy RJ 45 to RS-485

Hello,

with the change from EGX100 to EGX150 RJ45 also the connection port changes. A customer wants to connect a symmetra mw with modbus serial. Which Cable of RJ45 should be used for TD+ and which one for TD- ?

Connection on EGX150:

Connction on Symmetra MW:


Accepted Solutions
Daniel_Borle
Commander Commander
Commander
0 Likes
0
127

Re: EGX 150 Pin occupancy RJ 45 to RS-485

Hi Sven,

Referred to the Link150 manual PIN 4 from Link150 must be connected to PIN 3 of Symmetra, PIN 5 of Link150 to PIN 8 of Symmetra and PIN 8 of Link150 to PIN6 of Symmetra:

Link150.png

See Answer In Context

2 Replies 2
Daniel_Borle
Commander Commander
Commander
0 Likes
0
128

Re: EGX 150 Pin occupancy RJ 45 to RS-485

Hi Sven,

Referred to the Link150 manual PIN 4 from Link150 must be connected to PIN 3 of Symmetra, PIN 5 of Link150 to PIN 8 of Symmetra and PIN 8 of Link150 to PIN6 of Symmetra:

Link150.png

Sven_Ortmann
Commander Commander
Commander
0 Likes
0
127

Re: EGX 150 Pin occupancy RJ 45 to RS-485

Hello Daniel,

Thank you I found the documentation yesterday:

https://www.schneider-electric.com/en/faqs/FA323145/