Hello,
with the change from EGX100 to EGX150 RJ45 also the connection port changes. A customer wants to connect a symmetra mw with modbus serial. Which Cable of RJ45 should be used for TD+ and which one for TD- ?
Connection on EGX150:
Connction on Symmetra MW:
Link copied. Please paste this link to share this article on your social media post.
Hi Sven,
Referred to the Link150 manual PIN 4 from Link150 must be connected to PIN 3 of Symmetra, PIN 5 of Link150 to PIN 8 of Symmetra and PIN 8 of Link150 to PIN6 of Symmetra:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello Daniel,
Thank you I found the documentation yesterday: