Com'X510 Negative Power

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Com'X510 Negative Power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
Koen_Rowies
Lt. Commander Koen_Rowies Lt. Commander
Lt. Commander

Posted: ‎2017-02-24 07:24 AM

0 Likes
6
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-02-24 07:24 AM

Com'X510 Negative Power

Hello,

I have noticed that Com'X can not visualise negative"Active Power", hystorical trending freezes when you want to visualise:

ScreenHunter_83 Feb. 24 16.01.png

ScreenHunter_83 Feb. 24 16.00.png

That's a pity, you can not use a com'x when you have both received and delivered energy or negative and positive power

Is this a known issue?

Kind Regards

Koen

Tags (3)
  • Tags:
  • com'x 510
  • energy
  • solar
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Anonymous user
Not applicable

Posted: ‎2017-02-24 10:39 AM

0 Likes
1
1882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-02-24 10:39 AM

Hi Koen,

Sorry to hear you're running into trouble, what version of the ComX510 are you using?

Best,

Colton Peltier

Reply
Koen_Rowies
Lt. Commander Koen_Rowies Lt. Commander
Lt. Commander

Posted: ‎2017-02-27 04:50 AM

0 Likes
0
1882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-02-27 04:50 AM

Hello Colton,

Firmware:

Tomorrow I will test this with the latest firmware in our lab.

Kind regards

Koen

Reply
Koen_Rowies
Lt. Commander Koen_Rowies Lt. Commander
Lt. Commander

Posted: ‎2017-02-28 05:07 AM

0 Likes
3
1882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-02-28 05:07 AM

Colton,

Did the test with firmware version

Here the same problem, no negative power...

Kind Regards

Koen

Reply
Anonymous user
Not applicable

Posted: ‎2017-02-28 06:18 AM

0 Likes
2
1882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-02-28 06:18 AM

Hi Koen,

I'm sorry you're experiencing this issue. I also tested on 3.5.15, and was able to recreate the exact issue you specified. When I tried our newest development snapshot of the firmware, I was not able to recreate the issue. I spoke with the engineering team, and they confirmed that this issue had been discovered and corrected recently. The fix for this issue will be included in our next release (Q2 this year). Here is a image of the corrected dashboard:

Negative_Historical_Trending_Snapshot_Build.JPG

Best Regards,

Colton Peltier

Reply
Sven_Ortmann
Sven_Ortmann Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-10-18 07:10 AM . Last Modified: ‎2025-06-11 11:32 AM

0 Likes
1
1882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-10-18 07:10 AM

Hello,

 

any news on this problem? because I have similar case on customer comx510

as you can see here: ComX510 does not show negative values at trend visualization  

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2017-10-18 09:29 AM

0 Likes
0
1882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-10-18 09:29 AM

Latest firmware version for the energy server COM'X 510 (Version 3.6.3)

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore